TimmyB

Hi All
Just come across new kitchen install with the old cooker cable extended to new position and a 13A socket wired in 2.5mm connected to the 6.0mm at old cooker position. Would you argee the 32A protection for this socket is a breach of Regs
 
Malcolm I agree about the loading bit but suppose a diyer wants to do something in there, knocks the sockets off and goes to work on that outlet. One dead diyer!
 
The requirment for the socket from reg 433.1 is surely a 20A device which cannot be compatible with the 32A cooker circuit
 
Malcolm I agree about the loading bit but suppose a diyer wants to do something in there, knocks the sockets off and goes to work on that outlet. One dead diyer!

There is that and there is also in appendix 15 that a cooker should be on it's own dedicated radial circuit, but as we know the appendices are informative except of appendix 1

Bottom line Trev I agree it was installed by an idiot
 
The A2 radial is a 32A circuit, The A1 is a 20A circuit, so the socket is relying on the downstream 13A fusing in the plug tops.
Think might ask installer for there paper work on this
 
You have it now Timmy the protection device at the CU is protecting the Cable mate. You will never in theory have more than 26amps at that 1 x double socket, and it would be amazing if you ever actually had half that at the socket at one time.

So though it is very bad practice for the reasons that Trev and I pointed out, providing you can adhere to the conditions of the regs and 433.2.2 in particular you could do it.
 
The installer can argue what the hell he likes in my opinion. Fact of the matter is it's wrong, shoddy, potentially dangerous and nothing that would be done by any competent electrician I know, which is why I'm betting there will be no paperwork in support of this crap.
People doing work like this should be buggered with something sharp and rusty.
 

Reply to Spurs before cooker Iso in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
436
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top