Hi, this is my first post so hope all who read my question understand it OK. Been to look at a job, Ring Final Circuit on 32A mcb all cables are with 2.5 T&E. The Circuit has 3 single socket outlets in a bedroom & are connected to 1 suitable Junction Box at the same point on the ring (3 spurs from 1 JB). I cannot access the JB without taking up the bedroom floor. My question is, a JB on a Ring Final is acceptable to connect 1 unfused Spur as per P.362 APP 15 in 17th Regs & P.54 IEE guide (Green Book) - BUT can the JB have more than one unfused spur taken from it at the same point in the ring & still comply as the circuit i have described above has 3 spurs from the same JB - is this acceptable under 17th Regs as i cannot find this answered within the forum or in my books. This may well be common on many old installs, but this JB with 3 spurs from it, is the first i have found to date. Many thanks in advance to any advice on this. My apologies if already discussed, let me know where to find within forum please.
 
Tricky one this and i have wondered this myself.

As you say, its not a lot different than having 3 JB's on the ring next to each other, with a spur from each.

My only concern would be successful termination if all three were from the same JB.

Five 2.5's in a 30A terminal is a tight squeeze.
 
Tricky one this and i have wondered this myself.

As you say, its not a lot different than having 3 JB's on the ring next to each other, with a spur from each.

My only concern would be successful termination if all three were from the same JB.

Five 2.5's in a 30A terminal is a tight squeeze.


Yes, i agree a tight squeeze indeed and if i could gain access to the JB, i would certainly ammend. But my Test results are suitable, so i have to take it that the connections within the JB are good. I know it is not good practice, but i take it from your answer that more than one 2.5 T&E unfused spur from a single JB on a Ring final is within the Regs if my Test results comply?
 
I came across this the other week and immediately thought I'd have to change it, then thought that no cable is at risk of overload at any point, it's no different from spurring off the same cable a foot further round. If terminations look good and reliable then I would leave alone. Also picked up some 5 pin wago connectors last week which would do this job perfectly. That must be what they're designed for too
 
it say,s one spur for each outlet.not one spur from each outlet.so three seperate spur,s from one jb no problem.what the regs are saying is dont have 10 sockets on a ring and 11 spurs not only run one spur from each point
 
as you have only one socket on each spur, i would say that although not ideal, it is acceptable. you are , as i saw in a previous post, not liable to overload the spurs.
 
as you have only one socket on each spur, i would say that although not ideal, it is acceptable. you are , as i saw in a previous post, not liable to overload the spurs.

Not liable to overload spurs, but could be overloading the ring - should really be trying to spread the load on a ring final evenly.

JB also needs to be accessible - so no good in it's present position.:)
 
better to use maintenance free, wacos or hellermanns. depends on if you can access the JB
 
Last edited:
Intrigued to know how you know it is from a single JB if you can't get to it:confused: - now if you have some diagrams for the installation that really would be a first !!! ;)
 
Its complant wiring wise but if it's a jd with screw terminals you need to acces it and you say you can't therefore it's non compliant
 
Thanks for all these replies, more than i thought i would get! The job is in a Bungalow, these usually have quite large voids under the floor area for ventilation and heating & due to this i could gain access under the floor in the hall. To cut a long story short, i was able to see under the floor of the Bedroom where i suspected a JB would be with my Torch, but could not get to it. Waynel is correct in his post and the JB must be accessable to comply, this can be done by taking up the bedroom floor boards over the JB, the customer is not to keen on this option and as my Test results are OK, - i will make a note of the JB's position on my Cert for future ref, am i correct in thinking this would then comply as long as the JB's position is recorded on the cert - in the end any JB can be accessed in a domestic property under wooden floors as long as the position is noted, only those JB's incased in cement or plaster are outside the regs. Any thoughts on this??
 
You haven't installed the JB, it tests out ok and you are marking its position on a cert - can't see that there is anything to be concerned about:)
 

Reply to Spurs from a Junction box on a Ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
589
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
659

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top