just been to look at a CU upgrade ( it's got a 16th board, 1 RCD for all ). on checking, found a couple of spurs off ring with 3 sockets on 1, and 2 sockets off other. not practical to ring these, or fit FCUs as recent expensive decoration been done. on checking the load situation on the ring, ( it's barely 12A with everything on ) i think , if i downrate the MCB to 16A, the circuit would comply. any thoughts appreciated.
 
dunno what the UK rules are on de-rating rings and FCU's feeding multiple socket outlets

can you split the rings into radials rather than de-rate them

you wouldn't want to cause tripping on overcurrent on kitchens etc. anyhow if you derated them
 
Last edited by a moderator:
kitchen ring not the issue. its the downstairs living rooms. highest load is the PC with it's associated bits
 
Last edited:
There is nothing stopping you wanting to fit a smaller protection device to the ring, though appendix 15 does clearly state what a ring final circuit is and denotes the protection as being 30 or 32 amps. So you would mark that on your EIC as a departure from the Regs and as your fitting a smaller protection device on a rated cable your not going to make the installation less safe and should be ok. Reg 120.3

Though if it was me you have no need to do anything really. As your fitting a new CU then all you need to do is make your work in line with the 7671. Again on your EIC you note in the part comments on existing installation the spurs and advise the client that they do not come up to the Regs and you advise them to have them upgraded.
 
I suppose if you down rate you would stop excessive load being drawn on those spurs but only by making the protective device operate. If only 12A on full demand id consider likely changes in that demand situation and make conclusion based on it. I think if sockets serve a kitchen/laundry you ll have to rethink.
 
comments appreciated. no changes anticipated. all sockets on spur are permanently plugged in items , vivarium, aquarium, PC, TV, 2 table lamps, all low power appliances. no heating, occassional hoover.
 
When you look at whats being used on a general circuit (not the kitchen ) then its very little may be a bedside light pc etc so id do as malcome has said derate the MCB to a 20 amp lable the board and identify on EIC
 
thank you both, malcolm and nick. just got to remember to unplug pc and tv before IR test!!!!!
 
There is nothing stopping you wanting to fit a smaller protection device to the ring, though appendix 15 does clearly state what a ring final circuit is and denotes the protection as being 30 or 32 amps. So you would mark that on your EIC as a departure from the Regs and as your fitting a smaller protection device on a rated cable your not going to make the installation less safe and should be ok. Reg 120.3

Though if it was me you have no need to do anything really. As your fitting a new CU then all you need to do is make your work in line with the 7671. Again on your EIC you note in the part comments on existing installation the spurs and advise the client that they do not come up to the Regs and you advise them to have them upgraded.

Appendix 15 is Informative and does not form part of the regs so down-rating a ring to 16A is not a departure IMO.

I would just note it on the cert. that it is a ring to avoid confusion in the future.
 
Last edited by a moderator:
Informative it maybe but as we wire ring final circuits in a minimum of 2.5mm we adhered to it.
Informative it maybe but as we still connect a ring start and finish at the CU we adhere to it
Informitive it maybe but as we feed one single or double unfused spur per socket it's adhered to.
Informative it maybe but as still advised RCD for additional protection under 411.3.3 522.6.6 and 522.6.5 we adhere to it.

And about 3 other informative parts we adhere to ,so when you derate a ring final from circuit from 30 or 32 amp it is a departure, well to me it is and should be noted
 
think i might split the ring and make it into 2 radials. 16Aeach, one on each RCD, no departures, less problems with nuisance trips. everyone's a winner!
 
Informative it maybe but as we wire ring final circuits in a minimum of 2.5mm we adhered to it.
This is a matter of current-carrying-capacity of cables, not the size of the OCPD.

Informative it maybe but as we still connect a ring start and finish at the CU we adhere to it
If it didn't start and finish at the CU it wouldn't be a ring circuit.

Informitive it maybe but as we feed one single or double unfused spur per socket it's adhered to.
Again, a matter of current-carrying-capacity to avoid overloading cables.

Informative it maybe but as still advised RCD for additional protection under 411.3.3 522.6.6 and 522.6.5 we adhere to it.
You are adhering to the above regulations, not Appendix 15.

And about 3 other informative parts we adhere to ,so when you derate a ring final from circuit from 30 or 32 amp it is a departure, well to me it is and should be noted

For something to be a departure then it needs to be a departure from an actual regulation.

Appendix 15 is not a regulation and AFAIK there are no regs stating that a ring circuit must be fed from a 30A or 32A OCPD.
 
Then nor are any of the appendix regualtions then as they are all informative.

Appendix 12 does not quote any regulation to adhere to or conform to. It does give values from a table but it never refers to a regulation, but we still work to it.

I must be in a vast minority as I have yet in all the years I have worked in the industry seen a design for a 20amp ring final circuit. Nor have I worked on a installation that as had a 20amp ring final circuit and I doubt I will. So if it's not forming part of the regs it is certainly non conforming to traditional design, perhaps we should note it under 120.4 as NEW INVENTIONS

As I have said I have no problems with a 20amp ring final circuit and if you want to be perdandtic then yes it might not be against the regs, but it states informative or otherwise that a ring final circuit should be 30 or 32 amps and I would personally mark it as a departure on an EIC.
 

Reply to spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
334
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top