Informative it maybe but as we wire ring final circuits in a minimum of 2.5mm we adhered to it.
This is a matter of current-carrying-capacity of cables, not the size of the OCPD.
Informative it maybe but as we still connect a ring start and finish at the CU we adhere to it
If it didn't start and finish at the CU it wouldn't be a ring circuit.
Informitive it maybe but as we feed one single or double unfused spur per socket it's adhered to.
Again, a matter of current-carrying-capacity to avoid overloading cables.
Informative it maybe but as still advised RCD for additional protection under 411.3.3 522.6.6 and 522.6.5 we adhere to it.
You are adhering to the above regulations, not Appendix 15.
And about 3 other informative parts we adhere to ,so when you derate a ring final from circuit from 30 or 32 amp it is a departure, well to me it is and should be noted