This has probably been talked about time and time again, but today following a board change I carried out some testing.

On every circuit, the R1+R2 result was higher than the Zs result.

How come???
 
Last edited by a moderator:
sorry, wasn't watching what I was typing.... what I meant to say was R1+R2 was higher than the Zs result........ on every circuit.

(I've corrected the starting thread now)
 
Last edited by a moderator:
that often happens. the R1+R2 are purely the circuit resistances, whereas Zs is that + Ze. now you measure Ze with the earth dissed from the installation. now when you reconnect the earth, you introduce parallel paths through the main bonding, water, gas, etc. this lowers the effective value of Ze and hence Zs, often to below the R1+R2 value.
 
I can understand connecting bonds can reduce Ze due to parallel paths, but I can't see how it can reduce the Zs value lower than the recorded R1+R2
 
think about ohms law and parrallel earths for example if you have 2 wires each measuring 20 ohms wired in parallel the resistance across those wires will be half of the rating so will be 10 ohms , this is the reason why parallel earth paths can reduce the Zs reading ,but the R1R2 reading will be as measured as you have taken these reading with out any parallel earth in the circuit ,as you would have disconnected the R1 and R2 from the board joined them together and tested at the furthest point

see what i mean
 
Last edited by a moderator:
To me, it still doesn't explain why the results were less than R1+R2. I think it must be my meter.


If I measure Ze with bonds disconnected, I'd get say 0.11 ohms. I then connect the water and Gas bonds, measure Ze again, and get perhaps 0.09 ohms. If I then measure the R1+R2 of a length of cable and get say 0.04 ohm and then connect this to the installation and measure the earth loop, surely I shouldn't be getting a result of say 0.03 ohms. But this is what was happening...
 
Last edited by a moderator:
it's not only parallel paths. it's the way measurements are taken. also, you have the internal bits of RCDsand MCBs affecting the Zs reading.
 
I've had this and thought my meter must be faulty, so had it calibrated. Even now still get similar readings.

As tel just said, it must be the workings of the meters that does it also.

Used to bother me a bit, but as long as my calculated values are within the maximums then i don't worry about it
 
if you think that's strange, i had one . a 16th ed install. RCD as main switch. Zs on all circuits around 350ohms. Ze was 0.2ohms. took a"Zs" on the CU live busbar, 347ohms. internal workings od RCD affecting the value to a ridiculous extent.
 

Reply to Srange results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top