I've just put up a stainless switch plate.
The plate itself is giving me a reading of 10-12v.
Its earthed, and I've disconnected the earth just to see if any difference in voltage but there isn't.
Checked cables, no nips on insulation, nothing touching back box, its not tripping RCD, even when I touch the plate.
I'm just wondering where this 10v is coming from.
Any ideas on where to start "faultfinding" on this one?
Trench dug, tin hat on.
 
Try testing with an analog meter, and see what reading you get then.

I'd put money on it as being 0V.

Inductance/capacitance/earth leakage at an accessory will all give a very low reading with a digital meter. There are volts there, but no amps (ok, it is such a very low milliamp current that any analog meter will not be able to read it)
 
I thought he was talking about an old style analog voltmeter, similar looking to an analogue IR meter.
I have a cheap digital pocket multimeter already, I'll pick an analogue meter up cheap from amazon I guess!
 
I've just put up a stainless switch plate.
The plate itself is giving me a reading of 10-12v.
Its earthed, and I've disconnected the earth just to see if any difference in voltage but there isn't.
Checked cables, no nips on insulation, nothing touching back box, its not tripping RCD, even when I touch the plate.
I'm just wondering where this 10v is coming from.
Any ideas on where to start "faultfinding" on this one?
Trench dug, tin hat on.

10-12 volts between what exactly?
 
Sorry Pete and snowhead.
10v was measured between two parts of the plate.
I got 236v from line to neutral and 12v between line and CPC.
It just seemed strange to me so I thought I'd ask you lot as I'm not exactly full of "experienced" lol
 
Surely if you work for an electrical testing company there must be someone who knows the appropriate tests to carry out? Daz
 

Reply to stainless finish switch plates in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
481
Good point but then regular plastic switches aren't permanently running a wireless network module inside. It just seems odd not to have an earth...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top