Stair Circuit Tripping RCD | on ElectriciansForums

Discuss Stair Circuit Tripping RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

Dave W

Evening All,

Installed a new dual RCD CU today, all dead tests were ok however once live everythings fine until the landing light's switched on and BOTH RCD's trip, anyone experianced this before, any suggestions anyone ?
 
Evening All,

Installed a new dual RCD CU today, all dead tests were ok however once live everythings fine until the landing light's switched on and BOTH RCD's trip, anyone experianced this before, any suggestions anyone ?
What do you mean has anyone experienced an Rcd tripping before? the answer to your question is a shared neutral between the downstairs and upstairs lights. You obviously have the 2 lighting circuits over the 2 Rcds and the shared neutral ensures the trips go. I thought any spark with any knowledge would understand this. If you are not an electrician my profound apologies.
 
Its a dual RCD board so what I meant was put both circuits on the same side of one of the RCDs you could put them on the same MCB .But I would still keep the circuits separate and sort the borrowed neutral out
No that won't work, if you have 2 circuits sharing a neutral you need to ensure the phase conductors to both circuits share the same over current protective device fella, think about it.
 
I suspect he means the same RCD which will stop the tripping if the neutral a are both on the same side of the board. However, the cowboy method of putting both circuits on the same MCB would actually be safer than the current situation....if you can't be arsed to fix the problem properly of course.

You can put both lighting circuits on same RCD but this does not solve the shared neutral problem

You mean on the same mcb not rcd?
 
Yes it is a cowboy method, I agree 100% with you Fella, but that said although an appalling result, better than connecting to 2 different MCBs. Your right though it needs sorting out.
 
Yes I agree sorry never made myself clear I would only put on to separate MCBs if I had sorted the borrowed neutral, But then of course with the borrowed neutral sorted out you could go back to using both RCDs :rolleyes4::rolleyes4: As said the cowboy method is an easier fix though
 

Reply to Stair Circuit Tripping RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
383
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top