Just been to a job in flat stairway where the lights are flicking when they are off. Their is
9 x 2d 28 watt fittings with all having emergency lights the switch is electronic push time lag switch. Some lights were not working change lamps so all lights are working still flickering when off except one (which looked like a new fitting) then I switched off the lights by the emergency light switch the emergency lights worked turned off the emergency switch the lights stayed off and the lights did note flicker.switched the lights on after the time period the lights went off then started to flicker again any idea what the problem is please
 
Some Numpty may have connected the newish fitting up wrong leaving a L in it and somehow losing it N ... the result is a floating N which charges the capacitors enough to strike the tube which then collapses the voltage and charges up again in a cycle.... check the new fitting connections.
 
Some Numpty has connected the EM light up wrong it sounds like its using the control gear of the lights as a floating N which charges the capacitors enough to strike the tube which then collapses the voltage and charges up again in a cycle.... check the new fitting connections too.
......

[ElectriciansForums.net] Stairwell lighting flickering
 

Reply to Stairwell lighting flickering in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for coming back to me, actually I have found out the reason, a bit of a schoolboy error really, should have known. The LED was a HIVE lamp...
Replies
2
Views
811
That does help, it shows that the problem is almost certainly in the way it is connected and not a problem with the fittings.
Replies
15
Views
1K
davesparks
D
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...
Replies
2
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks