Can anybody advice on cable size for 250Kw star delta motor, star delta starter supplied with 240mm 4 core SWA protected by 500a fuses. Would like to keep cables at 240mm but terminal box looks a bit small for 2 x 240mm SWA cables motor is rated at 400v 430Amp

Regard

ps this is my first time on forum like what I see so far
 
i am figuring on VERY rough calcs at about 360A per phase , which would make (again -off the top of my head calcs) cable size around 100mm

240mm looks like someone has been VERY generous

have you done any calcs for this?
 
mm, you need a splitter box beneath the incomer

no such thing as 100mm, its 240mm or maybe 95mm, or perhaps 175mm?

give me the motor output in hp , the running current and start details, i will give you cable size and protection fuses
 
Last edited by a moderator:
Again with VERY rough calcs and no information on de-rating factors I recon on 120mm 3core x2 and separate earth to give you more room in terminal box.
 
I like benji,s idea. Anyway a common way of calculating the cable size is to realize the current in the cables between starter and motor when running is 0.58 times the supply current. But dont forget , as someone as already said the correction factors. If you are installing in conduit you already have one factor ,grouping. The six cables are loaded so in affect you have two curcuits. Best of luck.
Daisy
By the way did i say that is some motor?
 

Reply to Star Delta Motor Cable Size in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top