Hi
I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a new one to suit the 22kw 400v motor having calculated the overload to be 22.04A going by the plated current saying 38A. 38*0.58
Fitted it all today but having troubles with the overload tripping out on starting in star (it needs a good 30seconds to reach speed) which isn't surprising seeing its drawing 60-70A over that time.
Have I sized something wrong? The old overload was on 43A which wouldn't protect the motor once its running in delta.
The only other thing I can see that's different is this one the overload is on the delta contactor where the star contactor connects to where as it was on the main before.
Hopefully I'm missing something very obvious.
Tim
Tim
- TL;DR