Hi,
I have a 90KW 3phase electrical motor. It is set up on the star/delta configuration for high current start ups. The problem comes when I start the motor. It is fine in star but when it switches into delta it will trip. It won't trip every time and when it does stay on it will run fine. But stop the motor and try to run it again and sometimes it will trip on delta. I have checked the phase windings,nice low values. Meggered it out- everything ok there. The circuit will switch just fine with no motor connected, so everything brings me back to an overload issue. The thermal OL are set correctly and the supply voltage is coming from a 500KVA Genset. Plenty of power and no problems there. I am in a cold climate so ambient temp is no a problem for over heating. Any ideas??
I have a 90KW 3phase electrical motor. It is set up on the star/delta configuration for high current start ups. The problem comes when I start the motor. It is fine in star but when it switches into delta it will trip. It won't trip every time and when it does stay on it will run fine. But stop the motor and try to run it again and sometimes it will trip on delta. I have checked the phase windings,nice low values. Meggered it out- everything ok there. The circuit will switch just fine with no motor connected, so everything brings me back to an overload issue. The thermal OL are set correctly and the supply voltage is coming from a 500KVA Genset. Plenty of power and no problems there. I am in a cold climate so ambient temp is no a problem for over heating. Any ideas??