K

Knobhead

A mate has asked me if I’d help him with a fault on a star/delta starter. It’s a beast of a thing 800HP closed transition change over. The starter even has it’s own 800KVA 11/.44KV transformer.

He’s sent a drawing but it’s that old it’s like trying to piece the dead sea scrolls back together. Could someone just confirm the sequence of these things for me, it’s been a long time since I had anything to do with them.

A/ main contactor closes
B/ star contactor closes (time delay)
C/ transition contactor closes (small time delay)
D/ star contactor opens (small time delay)
E/ delta contactor closes (small time delay)
F/ transition contactor opens

Apparently every so often the O/L’s trip opening the 11KV OCB (the O/L’s, P&B Goulds are wired to the OCB direct and not the contactors) at the transition point. All my mate says is there’s one hell of a flash and bang when it trips.

Any ideas would be welcome as well.
 
A hell of a bang at the point of transiton could be down to a phase reversal on the delta contactor or at the motor. Does he know if anyone has been changing things.
Could also be down to interlock failing between contactors which could be checked with motor off load.
 
I would have to be “He-Man” to change anything, from what I can make out on the drawing it’s wired in 400mm singles. I dread to think what the terminal box is going to be like with 6 of them going in!
Most of the time it starts OK it’s just the odd time it throws a wobbly. It seems the plant it’s on has changed operation so the motor starts 5 times a week now where it only used to start once a week. It’s got to the stage the plant operators have developed a nervous twitch when they go to start it.
Contactor interlocks are one of the first things on my agenda to check. I don’t know if there’s any sort mechanical interlock between them, I don’t even know what type they are yet.
 
Also consider the contactor points themselves with years of use they may have blasted away and now giving poor contact, with the sheer size of load the bang and flash may not be a short but just a poor contact point making under the high loading,,,, another thing to check is if the motor duty has changed and the so the motor is working harder this could be for many reasons, bearings belts blockage etc etc if this is the case then the star delta timings may be out and it may change over too fast which can give a massive surge, this can usually but not always be checked by listening to the motor reach its full speed which should be before the timer pulls in delta.
 
Well that was a fun few hours. I expected to be looking at the starter Sunday, but a knock on the door this morning said different.
It’s a beast of a thing! The contactors are old BHI things left over from building the ark. The contactors have 3 coils, 1 per phase to pull them in and opening coils fed by capacitors. It’s DC control just to add to the fun.
First we went through all the main contacts, not a mark on them except the star contactor. Each pair of contacts must weigh a ¼lb. All auxiliary contacts looked OK.
First test with the motor isolated the change over happened so fast we couldn’t keep a check on it so I increased the transition time. 2nd trial all seemed OK. Now came the fun, we’d got the panel door open and went for a start. Main & star closed OK and the motor ran up to speed. Came the transition the aux contactor closed which does cause a short circuit but the loading resistors control it. The delta contactor pulled in just as the star was opening. FIREWORKS! Dear god was it loud! I’m glad the O/L’s open the OCB and not the main contactor, I was about in need of a pair of pampers as it was!
Checked the star contactor to find a worn pivot bearing and a burnt connection on one of the opening coil capacitors. BHI panels always look neat, all the control wiring is run at the back of the equipment tray. Great until you’ve a duff connection to find. We also altered the star contactors delta interlock contact to give more clearance. In true BHI style even the aux contacts are adjustable.
Tried another 4 starts and all seems OK. The starter is limited to 2 starts per hour so to get around that we took the covers off the resistors and had a 24” fan blowing on them.
 
Not so much fun when you’re getting blamed for a 2000HP motor slip rings failing 6 times within 3 months. That turned out to be a batch of fault brushes, did anyone say sorry for having a go at me…… We even filmed the explosion, that was fun!
 

Reply to Star/delta starter in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Yeah, I've now got all that but with the electronic timer. The ABB AF contactors aren't compatible with the Schneider SD timer, but ABB don't do a...
Replies
17
Views
3K
Thank you, in the motor controls I have experience with this has been the usual set up I am used to, apologies for my ignorance. I will have a...
Replies
2
Views
4K
This is important. If the overload was originally connected in the supply lines it needed to be set to the 38A FLC, not the 0.58x FLC (22A) which...
Replies
19
Views
6K
  • Question
And here is the said schematic. This is the speed control section, showing the converter, drive motor, magnetic amplifier and related components...
    • Like
    • Informative
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks