Does anyone know how to correctly size the earthing conductor from the star point of a 11kV/433V distribution transformer to ground for its reference. I believe that I can use the maximum single phase to earth fault current and then give it a 1sec/3sec withstand time depending on client, Is this correct? I have asked around in my place of work and have been told half the size of the line/neutral conductor which I would accept if someone could tell me how you would work it out mathematically otherwise I think that there is a good chance that they would grossly over size this conductor.
TAke for instance the following example. HV LV earths are combined with the earth nest made up from 2x 70mm bare conductors surrounding the transformer. Now this is a maximum of 140mm. If there were 630mm tails away from the transformer and we halved the size of the line conductor that would give us a 300mm to use as the HV to LV link, now this to me seems daft as you are doubling the size of the actual conductors of the earth mat, that can't be right surely. To me there seems no logical point of having anything above that of the two tails coming from the earth mat.
Admittedly using single phase to earth fault currents to x seconds will also probably over size the cable but this could be used in a situation where the HV and LV need separation.
Any input is much appreciated.
Darren
TAke for instance the following example. HV LV earths are combined with the earth nest made up from 2x 70mm bare conductors surrounding the transformer. Now this is a maximum of 140mm. If there were 630mm tails away from the transformer and we halved the size of the line conductor that would give us a 300mm to use as the HV to LV link, now this to me seems daft as you are doubling the size of the actual conductors of the earth mat, that can't be right surely. To me there seems no logical point of having anything above that of the two tails coming from the earth mat.
Admittedly using single phase to earth fault currents to x seconds will also probably over size the cable but this could be used in a situation where the HV and LV need separation.
Any input is much appreciated.