Michelo Eugen

Am seeking for assistance on the above subject. What coukd be the problem when you swith on the start button the motor starts in star and when time for the delta comes the motor stops
 
Does the delta contactor energise when the timer times out? As spinlondon said, no delta connection to the motor (i.e open circuit). Could do with more info really.
 
Faulty contactor? blown overload fuses? Possibly drawing too much current on delta and blowing overload fuses which could be too much load for delta but not for star?
 
sounds like a timer switch over probklem as the motor is starting up but when switching to delta it stops you need to have a visual on the contactors to see what the problem is
 
Thank you all for your quick responce. Now how do i know that the timer is faulty? What happens is that after the timer has timed and time for the delta contactor has come , the motor will stop running and then when u press the stop button the sound of the de-enegising contactor will be heard(could not operate with open pannel because of Isolator which is the cover locker). The pannel type is telemechanique.
 
Well this looks like the faithful old bypass .......................but not recommended

Can you get a clamp meter anywhere on the circuit. When the motor starts you should get an high amp reading on the cables feeding the motor in star, this will be for literally a few seconds if that, then it should switch over to delta and you get the running amps.

Can you clamp meter anywhere?
 
Thank you all for your quick responce. Now how do i know that the timer is faulty? What happens is that after the timer has timed and time for the delta contactor has come , the motor will stop running and then when u press the stop button the sound of the de-enegising contactor will be heard(could not operate with open pannel because of Isolator which is the cover locker). The pannel type is telemechanique.

Well thats the hard bit you need to get a visual on the contactors and some people overide the main door interlock so they can see this but in your case if you have not done this before then leave well alone
 
Was this a working unit and recently failed?

Was this a working unit until someone worked on it?

Has anything been changed?


Have you tested through the motor from the bottom of the Line contactor to the bottom of the Delta contactor?

Is the timer a pneumatic, Line contactor mounted unit... or a seperate unit?

Has the timer been changed?

Are the interlock auxilliaries intact and operate as they should?

Is the Delta contactor coil intact?

Are all wires secure as to the diagram?

Is it this type of unit http://docs-europe.electrocomponents.com/webdocs/08fa/0900766b808fa434.pdf ?

A typical diagram http://docs-europe.electrocomponents.com/webdocs/0f0f/0900766b80f0f062.pdf !
 
Last edited by a moderator:

Reply to Stardelta connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've often wondered about this too. How useful are earth fault loop impedance tests/measurements when the motor has a VSD? I presume the fault...
    • Optimistic
Replies
3
Views
838
  • Question
Here are the other drawings
    • Optimistic
    • Funny
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top