DC motors are inherently capable of regeneration, and have been used with dynamic braking for a century or more. PM motors are the simplest - just short the terminals - car windscreen wipers usually park like this. Induction motors are not so easy because reconfiguring the supply to give reverse torque stands the risk of the motor starting up in reverse. So it takes an extra piece of kit, the rectifier (and transformer, if the rectifier is not phase controlled) to brake an induction motor. Of course with 4-quadrant PWM drive anything is possible. OP: look up 4-quadrant motor control.
 
But as said why only getting 230v motor connections,

why nit not just break live with e stops , forget control boards ...

There is a LOT more to it than that, the three items are, DOL starter, motor TM O/L, DC injection braking module.
The requirement is enshrined in the MD, and is stipulated in the various A, B & C type standards.
A bandsaw is an Annexe iv machine.
E-stops are NOT load switching devices, and must never be used as such.
The assembly is an SRPCS, thus it must meet certain standards, based on the relevant as I have said, A, B & C type standards for the machine and control system under consideration.
Looking at this I would also hazard that the machine is CE marked.
 

Reply to Starters and motors in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Well at about 9.30 last night I stripped the door card off and found the culprit, cable snapped and end off. So I spent another hour and managed...
    • Like
    • Funny
Replies
2
Views
233
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
566
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
97
That sounds to be more of a control issue rather that a motor issue Are all the limit switches working properly and not sticking occassionally
Replies
1
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks