static caravan supply | on ElectriciansForums

Discuss static caravan supply in the UK Electrical Forum area at ElectriciansForums.net

J

jimjamjimajam

Hi guys been asked to install some meters on static caravans today. When checking it out I found the homes are all fed from the same supply with a weatherproof enclosure below each one where the SWA is connected to t+e that feeds each van. Should these not have their each individual hook up points with RCD and over current protection?
 
Static homes are a real pain, they technically do not come under the 708 section of the Regs, but should be dealt with as a normal installation to the BS 7671. After all most static homes are not connected via a 16 amp plug but have a permanent hook up.

Again the IET have left things open when section is headed caravan/camping parks and Similar Locations

If a static home is not on a similar location then what is it on. I have always used the relevant parts of both the normal regs and the special location part to jerry pick the best installation.

Though the T & E is intriguing
 
Static homes are a real pain, they technically do not come under the 708 section of the Regs, but should be dealt with as a normal installation to the BS 7671. After all most static homes are not connected via a 16 amp plug but have a permanent hook up.

Again the IET have left things open when section is headed caravan/camping parks and Similar Locations

If a static home is not on a similar location then what is it on. I have always used the relevant parts of both the normal regs and the special location part to jerry pick the best installation.

Though the T & E is intriguing
Straight forward really malcolm surely?
 

Reply to static caravan supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
365
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top