need a few pointers with testing offpeak storage heaters CU
no prob with dead tests but what about the live tests Zs /Ze ?
don't think turning up at midnight when it comes live is an option :eek:
would you issue seperate test sheet for power/lighting CU & Offpeak CU or use a continuation sheet

elfyn
 
ze can be obtained by measuring at the main board, (it will be the same as the off peak)

zs can be calculated from this and r1+r2
 
cheers for the reply
i agree on the Ze being the same at both points but was lead to believe the measured Zs value was the way to go with the calculated Zs as a cross check.
offpeak CU also has an 80amp 30ma rcd main isolator any thoughts on testing it
elfyn
 
Calculated zs is fine but obviously you need power to test the rcd.
If its a pir you are doing you could make a note to say that you were unable to test it.
Otherwise it's a case of livening it temporarly or a midnight visit.
 
Calculated zs is fine but obviously you need power to test the rcd.
If its a pir you are doing you could make a note to say that you were unable to test it.
Otherwise it's a case of livening it temporarly or a midnight visit.
no its a EIC not a PIR ,changed both boards as they were old wylex rewirable's & the usual main earth gas & water incomer to 10mm as tncs supply.
tested everything apart form final offpeak CU measured Zs's & Main RCD
i left it locked off as no heating required at the moment but need to get it finished this week.
temp power lead it is then as i ain't doin a midnight run:p.
cheers elfyn
 

Reply to storage heater CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
Fantastic thanks Freddo that last photo confirms all your suggestions so I’ll get back over and remove the links and test. Thanks again!
Replies
4
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
573

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top