Hi, quick question for anyone who knows a bit about storage heaters. I was asked to check if an old one was working but it's on E7 and wasn't powered up at time of inspection. Next stage would be to power it up temporarily off the main board, but just for now I removed the flex from the connector unit and did two tests:
1. Low resistance test between L-N. This showed around 30 Ohms which I think is about right for an average size storage heater element - calculates to about 1.8kW - and should confirm the overheat link is intact.
2. IR test between L-E and N-E. I got a reading of 1.2 MOhms for both.
Are these normal results? I wasn't expecting the low IR results.
Cheers
1. Low resistance test between L-N. This showed around 30 Ohms which I think is about right for an average size storage heater element - calculates to about 1.8kW - and should confirm the overheat link is intact.
2. IR test between L-E and N-E. I got a reading of 1.2 MOhms for both.
Are these normal results? I wasn't expecting the low IR results.