Storage heater keeps blowing fuse | on ElectriciansForums

Discuss Storage heater keeps blowing fuse in the Talk Electrician area at ElectriciansForums.net

G

gaz26

Hi ya guys ,i wonder if you can help me.
Have just been called out to a robinson willey storage heater that keeps blowing the fuse in the cu, it is a combi heater, the convector heater is working fine off the peak but the storage heater on the off peak keeps blowing. Its a 3400w heater.
I have tested it resistance between p and n at the terminal at the bottom and get a reading of 15.2ohms which using the formula voltage squared divided by power and the reading is fine.
ie 230 x 230 = 52900 / 3400 = 15.5 ohms

The resistance on both elements between p and n is 30.3 ohms which i also deem fine.

Also the thermal cut out hasn't tripped so i dont think it has overheated,and both control dials are functioning correctly.

I have also PAT tested the storage side of the heater and it passes fine.

Ive checked the leg back to the cu which is feeding it and this is fine too(This has got its own designated circuit i must add protected by the 15amp cartridge fuse.

I guess what i want to know is ,is there anything else i can do to find and distinguish the fault ? and the only thing now i can think it may be is a dodgy element, which is blowing the cartridge fuse it out when it starts to warm up as this would explain why it PAT tested ok because the tests only last 5 secs .

If it is the element ,how can i tell which one as testing the resistance when it is off,they both have the same reading.

Any ideas would be very appreciated

Thanks in advance
 
it is possible a element that shorts out only when its hot, if you cant locate using basic insulation testing etc then try disconnecting one element at a time and see if it cures the problem it may take a couple of nights to sort or you could rig a temp supply on a mcb to check it out, visually check the stat and thermal cutouts too to see if there is any evidence of flash marks, overheated cables etc ...good luck.
 
have you checked insulation resistance to earth? it sounds as if you have with your pat tester. Also can you use an ammetre to check how much load it is pulling. You should be able to do this on each element and find the faulty one. Good luck
 
Last edited:

Reply to Storage heater keeps blowing fuse in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
188
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
580
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
538

Similar threads

And with a duff one, it just sits there, not knowing which way to turn, but drawing considerably more than its normal run current.
Replies
7
Views
373
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top