I have a 3.4kW creda storage heater tripping a Type 3 16A Federal mcb. I have insulation resistance tested both the supply circuit and the heater and all is fine and also fired it up on a plug top and it runs for 20 mins fine and trips no fuses at all. Its pulling around 14 amps so i would expect the elements to be fine and there is no visable signs of damage. Its only the next morning the client rings up and says the mvb has tripped. Is it possible the mcb has gone weak? or is there something else i am missing?
Any help much appreciated, cheers
 
A few years ago I got a call to a social housing complex with a similar problem.
after a few visits I tracked it down to a poor plug in connection on thr federal panel board.what a pile of cack that thing was.worth a try.failing that strip it down n visually check elements
 
Did you check the resistance of the elements or was that 14A measured?

Assuming the machine checks out okay for continuity values and IR (along with the circuit), then suspect the mcb. Is it installed with another device either side? Many manufacturers recommend a rating factor of 0.8 if loads are continuous and there is no air either side. If so it may have become "over sensitive" with age due to heating. If the cable is 2.5 and the install method will support it, change it to 20A.
 

Reply to Storage heater tripping mcb in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
511
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
458

Similar threads

  • Question
Fantastic thanks Freddo that last photo confirms all your suggestions so I’ll get back over and remove the links and test. Thanks again!
Replies
4
Views
1K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top