Question - a Dimplex 3.4KW storage heater would presumably have a max current drain of 14.78A. Given that 2.5mm T&E is rated at 20A on a radial, would it be ok to run it in 2.5 T&E on a 16A MCB? Reason I ask is that I have only ever seen storage heaters run in 6mm (maybe because there were more than one heater on the radial?)
I would be running each heater on it's own radial
Thanks
Andy
Question - a Dimplex 3.4KW storage heater would presumably have a max current drain of 14.78A. Given that 2.5mm T&E is rated at 20A on a radial, would it be ok to run it in 2.5 T&E on a 16A MCB? Reason I ask is that I have only ever seen storage heaters run in 6mm (maybe because there were more than one heater on the radial?)