andyww

Hi All

Question - a Dimplex 3.4KW storage heater would presumably have a max current drain of 14.78A. Given that 2.5mm T&E is rated at 20A on a radial, would it be ok to run it in 2.5 T&E on a 16A MCB? Reason I ask is that I have only ever seen storage heaters run in 6mm (maybe because there were more than one heater on the radial?)
I would be running each heater on it's own radial

Thanks
Andy
 
Just a bit of advice..
If the installation has more than this one heater and they are all in the same c.u [usual setup], then I would install a 20A c.b rather than the 16A. Reason being that when all the heaters are initially switched on the circuit breakers can be loaded close to their rated current..if the c.b is not of a high quality then they tend to heat up. this combination of warm circuit breakers in close proximity to each other can in the long term have a detrimental effect on the c.b .and in some cases it can also trip it under full load: hence the reason in this instance for advising the 20A c.b...more tolerance to the thermal trip .


spark1
 
I've only ever seen Storage Heating wired in 2.5 T&E. I guess if the rating was large it would need a bigger cable (4 or 6 mm) but norally in domestic there on 2.5's

A Question i have tho is, when testing you can only do the dead tests as the power doent come on till late. How do you carry Ze and PSCC/PFC test out to calc Zs?
 
I always rig up a temp supply from the general supplies consumer unit to the off peak c.u and carry out a full functional powered up test. Reasons being.........

1. Confirmation that all will be well when the teleswitch powers up ,usually when the residents are in bed...peace of
mind scenario !

2. To allow all coatings of heating elements to be burn off at time of installation preventing unwanted fumes possibly
circulating in rooms inhabited by sleeping persons....especially children.



spark1
 
Last edited by a moderator:

Reply to Storage Heaters Dimplex 3.4KW in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
576
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
428

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top