Hi Guys

I am new to the Forum so here goes......

We have been called to a Farm which is 40+ years old, it is a TT 3 phase supply and has a 100mA main RCD switch at the incoming supply.

There is a main DB in the barn and out of that is an SWA sub main which feeds a stable with only one lighting circuit on it. And one 400w SON and weatherproof switch.

We were called out as everytime the light is operated the RCD will trip.After some investigation and testing one of the cables had been chewed which feeds the light as the previous spark had wired it in T&E!

We have replaced the wiring to the switch and light and the light itself is in good working order.

The problem we have is that everytime we operate the light, the incoming SWA gland of the sub main cable will spark and go bang and trip the RCD.
No fuses have blown and the Lines to Neutral and Earth are all clear in the IR test.
I have got 230v from each Line to Neutral and Earth so all seems good.
Not sure what else it can be? - there is no load on the board only this SON fitting and there are no Eddy Current issues.
Does anyone have an idea what it could be?
I can distantly remember a similiar fault when i was an apprentice and im sure it was a loose/partially damaged neutral along the cable?

Thanks in advance for any help on this
 
Bust swa cable somewhere. Is it buried anywhere?
Sounds like the neutral and the armour earth are just about touching.... no fault showing up, but when a big enough load is put on, the return path is trying to use the armour.

40 year old electrics on a farm is unusual. Normally 60 - 70 round these parts.
 

Reply to Strange Fault on a Farm! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

Not to mention welding switch contacts together and wondering why when they thought they had got the wiring sussed the light will still not switch...
Replies
5
Views
558
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
736

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top