L

lister

newley installaed ring main with 15 socket outlets on it, ( just second fixed so nothing plugged in) when testing end to end resistances loop etc all ok but when insulation testing phase to cpc 48.0 meg neutral to cpc 148.0 meg and phase to neutral 250.0 meg
is the 48 meg result low enough to cause concern and any ideas ??
double checked every thing - all ok
 
Assuming you tested at 500V?

How long did you press the test button for?

Did the reading creep up?

Sometimes it can take a few seconds for the circuit to charge up.
 
all the readings are a pass but brand new i would expect the meter to top out >299 on mine at 500v
it may be worth popping the socket fronts off and having a look behind for pinched cables it will be hard to spot because the readings are not to bad
 
thanks for the replys chaps,
auto test so can only press once- if you see what i mean,(metrel 6557) tested several times reading stayed the same give or take a meg out of interest i did give it a blast at 1000V just for the hell of it and reading came back about the same?(just been calibrated as well)
checked every thing again- nowt. circuit now live and has been in use by builders all day ( touch wood no probs)
so would you worry about it or not.
 

Reply to strange ins res results?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top