W

welshsparky82

Was carrying out a periodic inspection today on a accomadation block....

testing the corridor lighting, which is made up of 28w 2D fittings, and Emergency bulkheads.

Went to carry out an earth loop test on the circuit, and wasnt able to.

checked supply at a fitting.

and was getting these voltages

L - N - 230v

L - E - 70v

N - E - 50V



Wandering, if anyone has come across something like this before, and could point me in the right direction..


cheers!
 
Switchgear could effect you test results ,It's going to be a pain but I would do an Zs and R1 R2
 
Last edited by a moderator:
Hi

Ye was about to start disconnecting fittings tomorrow.. its quite a large circuit, possibly 20-25 fittings on it.

so just wanted to see if anyone had come across this problem before...

was thinking dodgy fitting perhaps.
 
Hi

Ye was about to start disconnecting fittings tomorrow.. its quite a large circuit, possibly 20-25 fittings on it.

so just wanted to see if anyone had come across this problem before...

was thinking dodgy fitting perhaps.

No earth continuity at the fitting, guaranteed.

Mine's a pint for solving the problem... :D

(Only being so certain because it's come up quite a few times in the last couple of months, and there's no other way you would get readings like that apart from a floating earth)

Best way to find it would be to halve the circuit, check halfway if there is an earth. If there is, then check half again further along, and so on and so forth. If there is still no earth half way, check half back. It's the easiest way to check stuff like this, used to call it the split half technique back when I was doing electronic fault finding....

Of course, I would check you have an adequate earth reading at the board first, and also that the CPC for the circuit you are working on is terminated properly.
 
Last edited:
No earth continuity at the fitting, guaranteed.

Mine's a pint for solving the problem... :D

(Only being so certain because it's come up quite a few times in the last couple of months, and there's no other way you would get readings like that apart from a floating earth)

Best way to find it would be to halve the circuit, check halfway if there is an earth. If there is, then check half again further along, and so on and so forth. If there is still no earth half way, check half back. It's the easiest way to check stuff like this, used to call it the split half technique back when I was doing electronic fault finding....

Of course, I would check you have an adequate earth reading at the board first, and also that the CPC for the circuit you are working on is terminated properly.


what he said:D
 

Reply to Strange Lighting Fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
276
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
780

Similar threads

  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K
  • Question
Could be damage to the N core touching the fabric of the building but the CPC of that cable is insulated from both. I.E. a screw clipping the edge...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top