Hi all,

Got a call saying the RCD had tripped on a 16th edition board where all the sockets (2 rings) cooker and immersion heater were on 1 rcd.

Going through what was on at the time led me to the tumble dryer in the garage which proved to have a short neutral to earth.

My question is that when i was trying to find the fault all the circuits when turned on would trip the RCD, normal for a neutral to earth fault apart from the cooker circuit which would stay on????

Testing the cooker circuit the zs was 0.3 and it tripped out in the required time for the rcd test. Looked in the CU and all seemed well in there.

I dont understand why it would allow the cooker circuit to stay on?

Any ideas anyne?

Thanks for you help.

Gareth
 
Going through what was on at the time led me to the tumble dryer in the garage which proved to have a short neutral to earth.

My question is that when i was trying to find the fault all the circuits when turned on would trip the RCD, normal for a neutral to earth fault apart from the cooker circuit which would stay on????

If the fault is within the appliance then all other circuits should stay on.



oh, and welcome :)
 
Last edited:
Hi,

Thanks for the reply.

But with the circuits in banks (controlled by 1 rcd) even if the circuits are isolated by turning the mcb's off, if you touch the neutral to earth it will trip the rcd. It puts it out of balance.

Try it! I have done it many times working on dead circuits but knocking the rcd off by accidentally touching the neutral to earth.

Cheers
Gareth
 
The neutral earth fault in an appliance that is left plugged in, can result in the RCD firstly staying in,because there is not enough leakage to earth to trip the rcd
When a load from a seperate circuit that shares the RCd is applied
The load current will use the neutral earth fault of the appliance, and may cause there to be enough leakage to then trip the rcd
 
Ah ok yes,

So what your saying is there wasn't enough leakage current from the cooker circuit to trip the rcd but when the other circuits were turned on this was enough, i guess this is probably because the cooker circuit was wired in 6mm so it would be easier to use the cooker neutral rather than to find its return through the fault in the appliance.
Not sure if ive grasped this properly but i kind of get it.
Its a bit of a strange one i have never seen before and thought there must be some sort of explanation.
Have you seen this before des56?

Thanks very much for your help.

Gareth
 
suppose the fault you found on the tumble dryer caused a leakage current of say 25mA, this in itself would not trip the RCD. Say the cooker had a leakage current of 5mA or a bit more, then there's your 30mA to cause the RCD to trip.
 
Yes,
but this was happening whilst i was trying to find it, and once i did i was wondering why the cooker circuit would be on with the rcd on but all the other circuits would trip the rcd because of the neutral earth fault.
I think des56 probably hit the cause on the head, with the other circuits which share the rcd then puting a load current on the neutral sufficient enough too cause enough earth leakage to trip the rcd. But the cooker circuit not putting sufficient neutral current down to trip it. Im guessing that if i had used the cooker it probably would also have tripped the rcd.
Confusing!!!!
Thanks for all the answers.
Gareth
 

Reply to Strange RCD behavior, anyone got any ideas. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
204
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
664

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top