Strange voltage readings | on ElectriciansForums

Discuss Strange voltage readings in the UK Electrical Forum area at ElectriciansForums.net

J

Jjm

Been to look at lights today that was not working properly. After investigation I think the problem is in a switch which seems to have a feed from the downstairs lights and what I thought would be the loop to the next lighseems to have a voltage from the upstairs lights. When I put my tester across p-e of the cable from the upstairs feed I got reading of p-e 230, n-e 5v and p-n 189v. Can anyone explain the 189v between p-n.The two feeds where joined together in the switch like a loop in and loop out but when disconnected the upstairs lights do not work apart from an occasional flash of a low energy light fitting
 
Hello mate,

It could be a loose neutral somewhere along the circuit. Have you checked all other switches/lights (wherever the feeds are)? I had some LED's that would intermittently flash and eventually I found there was a neutral that had been pulled out of its terminal block, once put back in they all came back on! Anyway just a thought!
 
i wouldn't worry about the 5v at 1st. it's the 189v that's the problem. i suspect a poor connection on the neutral further upstream.
 

Reply to Strange voltage readings in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top