Hi people

I got a strange reading when doing a Ze test which no one else in the company could explain.

When the main earth to the house was disconnected I got a result of 11.08ohms
When I did the test with it reconnected to the house I got a result of 0.25ohms
When I tested the house with the main earth disconnected I got no result

It wasn't poor connection of the probes, or a failing battery in the tester.

When I started electrical testing I tested a few houses with parallel earth paths in place to see what happened, and always there was barely any difference in the results. I'm flummoxed.

The boss says to leave it and just use the 0.25 reading. However, I don't like leaving it if I don't understand the reading, so any opinions would be much appreciated.
 
I'd put money on parallel paths as I've seen lots of vastly different readings with bonding connected. What's the earthing system on this mate?
 
it sounds to me like your relying on your main bonding and other paralell paths for your earth path. If you getting 11.08ohm with the main earth disconnected, on a TNS or TNC-S system, then a phonecall to the DNO is in order.
 
Cheers
It's a TNCS
I've never seen that different results when I played around with the tester in the past.
Would you contact the DNO about the Ze or except the Zs as good?
 
Measure it with a different tester and main earth disconnected so that you know that it's just the Ze you're measuring, if it's too high for a TN-C-S then get on to the DNO. I wouldn't accept anything that I wasn't certain about mate
 
weird, can you see the earth cable go into the DNO head from the cu. As its TNCS you would expect a proper reading but that does rely on the earth wire making it back to the head end. Could also be loose / fall out inside the head but seams unlikely. Not right anyway
 
Hi people

I got a strange reading when doing a Ze test which no one else in the company could explain.

When the main earth to the house was disconnected I got a result of 11.08ohms
When I did the test with it reconnected to the house I got a result of 0.25ohms
When I tested the house with the main earth disconnected I got no result

It wasn't poor connection of the probes, or a failing battery in the tester.

When I started electrical testing I tested a few houses with parallel earth paths in place to see what happened, and always there was barely any difference in the results. I'm flummoxed.

The boss says to leave it and just use the 0.25 reading. However, I don't like leaving it if I don't understand the reading, so any opinions would be much appreciated.

It must be me, because the rest of the lads have had a go at answering, but for me that as totally threw me.

If it is a TNC-S did you test L-N to see what you got? If you did and you got the same results then you need to contact the DNO they have a real problem.
 
When the main earth to the house was disconnected I got a result of 11.08ohms
When I did the test with it reconnected to the house I got a result of 0.25ohms
When I tested the house with the main earth disconnected I got no result
After reading Malolm's post I realise those 3 statements are contradictory 11.8 ohm with main earth disconnected then nothing???
 
There are a good few replies. It is as simple as this.

Isolate the consumers side of the Installation at the main switch.
Disconnect the main earthing conductor after the supply head at wherever it is connected to, earth block, CU or whatever.
Do your Ze test, if it is in excess of 0.35 ohm, you have a problem, get the DNO out to it pronto.
If the installation remains energised, then it is imperative on a TNCS system that all the main bonding is in place.
If the main bonding is not in place then you have an even more serious problem, and energising the system could be life threatening.

Cheers..........Howard
 

Reply to Strange Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top