Hi chaps.... sorry, been busy digging ;)

@ Mogga :- Yes, condensation is one of the reasons I'm reluctant to use the RCD, during early spring the inside of these columns becomes a wadi!! My current plan is to go for as highly rated an RCD as I can get away with.

@ Pjay :- Unfortunately, dont think this will be of any benefit in this situation..... The installation is pretty much a straight line, with the first post being just less than half way along it!

I should probably put the situation into context more for all you helpful chaps :)
The streetlighting installation is on an MOD airbase and is about 40 - 50 years old. It was originally wired in 16mm ish PILC which as mentioned is in death throws!! 16 years ago, contractors were asked to add another 16 posts to the circuits totaling about 25 in all. This circuit is fed from a feeder piller (32A BS88), through a contactor (which is part of the site blackout system for aircraft, which is operated remotely) and then out on 3 core SWA (2 live conductors (both same phase) and 1 Neutral, with sheath as cpc). This links up with the PILC at some point underground and feeds the 25 odd columns (12 to the west of the origin and 13 to the east, covering about 1/3 mile in each direction (yeah I know!!). The entire circuit looks a bit like an H with the origin in the middle. I have the test sheets from 16 years ago when the extra columns were added (on a minor works cert!) which show a Zs of nearly 40 ohms!!!!! Apparently this was acceptable?!?!?! I've spent an age trying to trace this cable with a Cat & Genny (no records/plans available!!) but due to the cable being run close to data, drainage and foul water, LV and mostly HV cabling, the first 4 exploratory digs have proved fruitless (or my cat and genny work is REALLY bad!!) Fridays dig has turned up the first underground T joint (to a post). I'm going to split this and test the main each side to see whats usable and whats not. Im not expecting any of it to be, and the digging is mainly to appease the bean counters who want me to use as much of the PILC as possible to keep costs down.
The part of the circuit I'm installing the new supply to, consists of 6 columns which were added beyond the extremity of the original circuit. I think it would seem obvious to most of us that it needs to be started from scratch, but the bean counters obviously want this done on the cheap (which is why we're in this trouble to begin with!!).

Hopefully this has put it into context a bit more, but basically I'm expecting to run supplies out from the contactor to power up various parts of the circuit, with lots of SWA run along walls and the minimum of trenches :( All I can do is make the best of yet another MOD 'bad job'!!

Cheers for the help so far.... TS
 
I have scans of the relevant highway furniture regs somewhere....I'll dig em out and post them when I find them.

There are a number of additional 'requirements' set out in these regs and they do get quite picky about it all.

Are these columns to be adopted by your local authority upon completion.

Would be very grateful! No, its private network so additional council requirements shouldnt be a problem.... was looking for something to show a lesser requirement for loop readings.... the council seem to think anything below 13 ohms is fine!?!?
 

Reply to Street lighting... Help appreciated!!! in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
596
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

@DefyG is right... I'm not fully sure what your boss is after as when doing single line diagrams I usually show the whole installation. Anyhow I...
Replies
4
Views
515
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...
Replies
7
Views
449

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top