N
Nomad
Hi,
I am not familiar with the last bs7671 and have never carried out street lighting design.
I am trying to carry out calc for a street lighting system using 9 nos 150 w hit/hst lamp per radial circuit. Each run of the circuit length is approx 150m.
I have optd for 16Amp type D mcb for each circuit, 3 core 6sqm cable.
Volt drop for the circuit is within the limit.
The feeder pillar is likly to be connected to clients LV panel.
Can anyone tell me that it is a standard practice to have fuse (6amp) for each pole?
Problem:
Amtech is generating errors
1.exceeding 5 sec disconnection time
2. Fault current is high
Solution
1.Rcd for each circuit
2.But unable to reduce the fault level. Does this mean I need to replace the 16amp mcb with bs88 fuse.
Is there any other way I can address the both or I simply ignore the high fault current.
I am not familiar with the last bs7671 and have never carried out street lighting design.
I am trying to carry out calc for a street lighting system using 9 nos 150 w hit/hst lamp per radial circuit. Each run of the circuit length is approx 150m.
I have optd for 16Amp type D mcb for each circuit, 3 core 6sqm cable.
Volt drop for the circuit is within the limit.
The feeder pillar is likly to be connected to clients LV panel.
Can anyone tell me that it is a standard practice to have fuse (6amp) for each pole?
Problem:
Amtech is generating errors
1.exceeding 5 sec disconnection time
2. Fault current is high
Solution
1.Rcd for each circuit
2.But unable to reduce the fault level. Does this mean I need to replace the 16amp mcb with bs88 fuse.
Is there any other way I can address the both or I simply ignore the high fault current.