Hi all,
Just running through the "Photovoltaics in buildings guide - 2nd edition", as you do, and can't get my head around the string cable requirements.
p 16, 2.1.5 says:
"For a system of N parallel connected strings, with each formed of M series of connected modules, string cables are to be rated as follows
a. Array with no string fuses (of three or fewer strings only)
Cheers
Just running through the "Photovoltaics in buildings guide - 2nd edition", as you do, and can't get my head around the string cable requirements.
p 16, 2.1.5 says:
"For a system of N parallel connected strings, with each formed of M series of connected modules, string cables are to be rated as follows
a. Array with no string fuses (of three or fewer strings only)
Voltage: Voc(stc) * M * 1.15
Current: Isc(stc) * (N-1) * 1.25
b. Array with string fusesCurrent: Isc(stc) * (N-1) * 1.25
Voltage: Voc(stc) * M * 1.15
Current: Isc(stc) * 1.25"
Are the Current ratings there not the wrong way round? - if I have 1 string then I use the calc's in 'a.' so the rated current would be zero (i.e. Isc(stc) * (1-1) * 1.25).Current: Isc(stc) * 1.25"
Cheers