Could anyone clear this up for me. If you have lightining protection on a steel framed building is it still necessary to bond the structual steel work as the lighting protection is bonded all around the building. Or is the lighting protection classed as supplementary bonding and you should still bond structual steel. Seems a bit of a grey area and i've been told differently from different people.
 
I was under the impression that the lightning protection had a connection back to the main earth terminal to give the same potential. But i would say that as it is a seperate part of the installation maybe done by a specialist contractor that it should be bonded directly from the MET.
 
The structural steel must be main bonded back to the MET
Lightning protection should also be main bonded back to the MET...(I've never been able to understand the reason for this given that it never enters the equipotential zone)....BUT,main bonding of the lightning protection should only be undertaken after consulting a lightning protection specialist.
 
Last edited by a moderator:
Lightning protection is not connected to the MET but to the natural earth.

Bonding for structural steelwork should be installed as normal.

In Cuba we were working in a large metal sided building and on our spec it stated that lightning protection system had to be insulated from building metalwork with insulated clamps.
 
Lightning protection is not connected to the MET but to the natural earth.

Bonding for structural steelwork should be installed as normal.

In Cuba we were working in a large metal sided building and on our spec it stated that lightning protection system had to be insulated from building metalwork with insulated clamps.

don't know much
but i though structural steel and lightning rods were connected to prevent flashover/fire
 
Thanks for all your replies, i've spoken to our consultant and he's said that main structual steel bond back to MET and bond lighting protection to building and through earth spike at the end of each tape. Thanks again Paul
 

Reply to Structual steel/ lighitning protection bond in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
691
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top