Hi, just wondering if anyone thinks if this would be alright for a basic structure to a question in a 2391 exam asking how to carry out a "Continuity of Protective Conductors Test Method 1". Thanks in advance.
Dan.
Continuity of Protection Conductors (Including Main and Supplementary Bonding) – Method 1
1. Select a Low-resistance Ohm Meter, checking the battery condition, lead condition and up-to-date calibration certificate.
2. Isolate Circuit to HSG-85 requirements and place signs/notices and barriers where appropriate.
3. Connect the line conductor to the protective conductor with a temporary link at the distribution board or consumer unit to include all of the circuit.
4. Test between line and earth terminals at each outlet on the circuit checking for continuity.
5. Remove Temporary link between line and protective conductors at distribution board/consumer unit.
6. Record the result at the circuits extremity as “(R1+R2)” value on the schedule of test results
Dan.
Continuity of Protection Conductors (Including Main and Supplementary Bonding) – Method 1
1. Select a Low-resistance Ohm Meter, checking the battery condition, lead condition and up-to-date calibration certificate.
2. Isolate Circuit to HSG-85 requirements and place signs/notices and barriers where appropriate.
3. Connect the line conductor to the protective conductor with a temporary link at the distribution board or consumer unit to include all of the circuit.
4. Test between line and earth terminals at each outlet on the circuit checking for continuity.
5. Remove Temporary link between line and protective conductors at distribution board/consumer unit.
6. Record the result at the circuits extremity as “(R1+R2)” value on the schedule of test results