Hello

I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers.

I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean?

Say I had a 32A Type B would it trip over any current over 32A or would it trip at 32 x 3 = 96A as this is the three times the rated current?

Thanks

Jonathan
 
Hello

I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers.

I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean?

Say I had a 32A Type B would it trip over any current over 32A or would it trip at 32 x 3 = 96A as this is the three times the rated current?

Thanks

Jonathan

Yes you are correct. A 32A Type B miniature circuit breaker should not trip in less than 0.1 second and not more than 5 seconds with 3*In. A current equal to 5*In should trip the Mcb in less than 0.1 seconds.

Regards

Buckfast
 
Thanks to all!

So it trips quicker if the current is 3-5 times. One last question.

If I have a shower that is rated 8.5Kw Ib= 8500/230= 37A. How is a 32A type B suitable? Is it because the shower won't draw the full load? And if so, why won't it?

Thanks
 
Thanks to all!

So it trips quicker if the current is 3-5 times. One last question.

If I have a shower that is rated 8.5Kw Ib= 8500/230= 37A. How is a 32A type B suitable? Is it because the shower won't draw the full load? And if so, why won't it?

Thanks
I would say 32A Mcb not suitable. A 40A would be more appropriate. With regard trip times, The larger the overload/fault current the quicker the Mcb will trip
 
433.1 specifically precludes the example of using a 32A breaker for a 37A load: "Every circuit shall be designed so that a small overload of long duration is unlikely to occur."

More specifically. 433.1.1 (i): "The rated current or current setting of the protective device (In) is not less than the design current (Ib) of the circuit."

Looking at Fig 3A4 in the regs (p 325), looks like the 32A breaker might never trip at currents upto about 40A (ish, maybe a bit more). But the regs above say you shouldn't do this.
 

Reply to Student BS60898 Type B trip question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
307
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
367

Similar threads

  • Question
Received guidance from a logical soul on the Kawie Riders forum: Acc Fuse Block Power to BAT LOAD, install new cable from BAT LINE to AUX + (and)...
Replies
1
Views
352
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
203

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top