Why do circuits over 32A have a 5s disconnect time yet those 32A or less have a .4s disconnect time? I have read the relevant regs but do not understand why and cannot find the answer in my books
 
It's mainly to provide discrimination between protective devices, partly to do with cost and very slightly to do with safety.
Most circuits above 32A are used for distribution to final circuits. As such it is preferable for a fault occuring on a final circuit, not to cause the protective device for the distribution circuit to operate.
Some circuits above 32A are final circuits, but as they are generally used to supply fixed equipment, the likelyhood of damage occurring to flexible leads is slight, and the cost of providing a 0.4s disconnection time prohibitive. Also many of these circuits are required to be additionally protected by a 30mA RCD, so the disconnection time becomes rather moot.
It used to be in the 16th, that the 0.4s disconnection time only applied to circuits supplying socket-outlets or other circuits supplying hand held or portable equipment.
Obviously a 0.4s disconnection time is safer than a 5s disconnection time. Lighting circuits were allowed a 5s disconnection time.
The 0.4s disconnection time was extended to cover lighting circuits in the 17th, to provide greater safety, probably because of the increase in the use of metal light switches, and the increased use of socket-outlets for connecting standard lamps and table lamps etc.
 
still see test sheets where the electrician has entered 5 secs. for lighting.
 
as spin said! if you tried to get a Zs on a large feeder low enough to allow a shorter disconnection time, thecable size wouldhave to be largher, and your talking lots of money!
 
Yes johnboy. Understood that. Point was that the regulations aren't concerned with cost, they are there to govern safety. I knew there must be a practical reason.
 
vested, also include suited, tied, shirted, kept in booze, mistress in £1m apartment, bi-annual thailand trips........
 

Reply to Student doesn't understand disconnect times in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694
Yes, probably overthinkig, thanks.
Replies
6
Views
599

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top