Why do circuits over 32A have a 5s disconnect time yet those 32A or less have a .4s disconnect time? I have read the relevant regs but do not understand why and cannot find the answer in my books
 
It's mainly to provide discrimination between protective devices, partly to do with cost and very slightly to do with safety.
Most circuits above 32A are used for distribution to final circuits. As such it is preferable for a fault occuring on a final circuit, not to cause the protective device for the distribution circuit to operate.
Some circuits above 32A are final circuits, but as they are generally used to supply fixed equipment, the likelyhood of damage occurring to flexible leads is slight, and the cost of providing a 0.4s disconnection time prohibitive. Also many of these circuits are required to be additionally protected by a 30mA RCD, so the disconnection time becomes rather moot.
It used to be in the 16th, that the 0.4s disconnection time only applied to circuits supplying socket-outlets or other circuits supplying hand held or portable equipment.
Obviously a 0.4s disconnection time is safer than a 5s disconnection time. Lighting circuits were allowed a 5s disconnection time.
The 0.4s disconnection time was extended to cover lighting circuits in the 17th, to provide greater safety, probably because of the increase in the use of metal light switches, and the increased use of socket-outlets for connecting standard lamps and table lamps etc.
 
still see test sheets where the electrician has entered 5 secs. for lighting.
 
as spin said! if you tried to get a Zs on a large feeder low enough to allow a shorter disconnection time, thecable size wouldhave to be largher, and your talking lots of money!
 
Yes johnboy. Understood that. Point was that the regulations aren't concerned with cost, they are there to govern safety. I knew there must be a practical reason.
 
vested, also include suited, tied, shirted, kept in booze, mistress in £1m apartment, bi-annual thailand trips........
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

mhar

Arms
-
Joined
Location
devon

Thread Information

Title
Student doesn't understand disconnect times
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
mhar,
Last reply from
telectrix,
Replies
7
Views
5,136

Advert

Back
Top