A

ab1978

hi all

have any of you heard of a fire alarm having to be installed in a house that is being used for student accommodation? local council has told owner it has to be in fp200 breakglasses panel in entry zones etc. Its just a 4 bed terrace, building control are involved because he's done a loft conversion. seems so over the top and i do alot of student properties and they have wired smokes only. have anyone else come across this.
 
It sounds like loft conversion has pushed it over the edge into HMO territory, if so, then its a full on Fire Alarm, emergency lighting, and usually full PIR if its out of date, and the best bit, The HMO office can force them to have everything up to the latest wiring and building regs, or they get fined big time and dont get their HMO licence. You need to speak to the planning dept concerned to get the full info as the rules do vary a bit from council to council.

Cheers.........Howard
 
Getting this all the time, first thing to ask local authority is which grade of system do they require, then ask if they are untertaking the risk assessment. Also state if so then they are responsible for the design. You will then find they back down very quickly.
I personally would state from your message that this would be classed as a HMO Grade D LD2 systems, and standards AICO or equiv. detection is more than adiquate. Make shure all design certs relate to Local Authority specs and requests...they hate that..!
 
Well worth a look at www.aico.co.uk full range of linked wired and radio fire detection to meet part 6. We fit 60 odd units per month in HMO and would recommend them for ease of installtion, check out radio call points make life a lot easier in converted housing. if you need any tip give me a pm
 

Reply to student house and fire alarm installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
789
  • Question
I've looked at the fire assessment from the last HMO I did for the same landlord and fire assessor, the risk assessment is pretty worthless, it's...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top