Some test instruments display a prospective fault current reading when carrying out an earth fault loop impedance test. Please can someone tell me why the pfc test must be carried out as a desperate test from an external earth fault loop impedance test?

My exams are near by I will be much obliged if someone can explain this to me. Thanks.
 
The Earth Fault Loop Is as it says The Impedance (resistance) of the Earth system.
But the Prospective fault current PFC is the current that will run in a dead short situation, so this should be tested between L and E and L and N as a dead short between L and N could give a greater value.
And on 3 phase systems a short between L and L would be even greater. A rule of thumb on 3 phase is to do L-E and L-N of all 3 phases take the higest reading and double it.
Good luck with the Exam
 
^^^......plus the reason for testing is because the PFC should be less than the breaking capacity of the protective device. If you look at a typical MCB or fuse it will be marked with it's breaking capacity,usually something like M6. This means a breaking capacity of 6ka....or 6000 amps. The measured PFC at the origin of the circuit must therefore be less than 6ka or the MCB will not be capable of breaking a dead short fault current.
 
Some test instruments display a prospective fault current reading when carrying out an earth fault loop impedance test. Please can someone tell me why the pfc test must be carried out as a desperate test from an external earth fault loop impedance test?

My exams are near by I will be much obliged if someone can explain this to me. Thanks.

The PFC/PSSC can be carried out at the same time as the Ze. Most instruments do this anyway. I don't know why you have been told otherwise. There is nothing to be gained by doing it separately, and in any case ohms law never lies, so you could get away with not doing it at all in reality. In all the testing course i have run, i have never made anyone do this separate to Ze, but i do make them calculate after to ensure that they can substantiate their results.

Cheers.............Howard
 
Ze is carried out Line to the earthing conductor whilst the earthing conductor is disconnected from the installation.
PEFC is carried out with the main earthing conductor connected to the installation and with the parallel paths that may be created by bonding, etc.
 
just to muddy the water. why do we measure PFC with bonding connected? answer.. to give the worst ( highest ) result. then from the 2 readings, PSCC and PEFC, we record the highest, which is always PSCC excepting TNC-S , where they should be the same. now, the PSCC (L/N) will not be affected by the bonding, so what's the point? i throw this out for discussion, if anyone's bothered.
 
N6rul
From the point of view of your exam;
PFC is at the origin of the installation for the reasons others have given - can the fuse and the earth conductor cope with that much current.
EFLI is at the furthest point of a circuit to give a worst case earth fault current and hence tripping time.

Think about a TT installation; The PEFC may only be a couple of amps but the dead short - line to neutral, would be hundreds of amps.

Hope that's helpful
Laurie
 
How would i write it in exam

Sorry guys being a bit cheeky. During the exam you get only only 2 mins to answer the questions, what would be the best way to answer this question. I understand the earth fault loop test is to determine how much current can go through the protective conductor in the event of a fault. And the Pefc is to check if the protective device ie Rcd is sufficient if a fault occurs.
Is this correct.
 
Re: How would i write it in exam

Some test instruments display a prospective fault current reading when carrying out an earth fault loop impedance test. Please can someone tell me why the pfc test must be carried out as a desperate test from an external earth fault loop impedance test?

My exams are near by I will be much obliged if someone can explain this to me. Thanks.

Sorry guys being a bit cheeky. During the exam you get only only 2 mins to answer the questions, what would be the best way to answer this question. I understand the earth fault loop test is to determine how much current can go through the protective conductor in the event of a fault. And the Pefc is to check if the protective device ie Rcd is sufficient if a fault occurs.
Is this correct.
If your question is as above "Some test instruments display a prospective fault current reading when carrying out an earth fault loop impedance test. Please can someone tell me why the pfc test must be carried out as a separate test from an external earth fault loop impedance test?"

Then the answer would be:
Each is measuring the worst case scenario: external EFLI measured using only the main earthing conductor gives the highest resistance in relation to the maximum external EFLI allowed.
PEFC measured with main equipotential bonding in place as well as the main earthing conductor gives the maximum fault current in relation to the short circuit capacity of the protective device(s).
 
thanks

I'm just loving it, this is the first forum that I have received x amount of help. Invaluable to a student like myself and others in my shoes..Thanks :D
 

Reply to student need help please re: pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top