Hello everyone,

I am working on my C&G 2357 unit 304 task A and one of the questions is:

Determine the minimum cross-sectional-area(csa) for each of the following:
a) earthing conductor, where the incoming live conductor are 25mm2.

I am up and down the regs and web to find something on this, and all I found is this formula:
S =​
Ö(Ia²t)
k​
can someone please direct me right way on this please...

Thanks
 
If you have been given no information on protective devices and their characteristics then you cannot calculate using the adiabatic equation.
Based on the information given, look at table 54.7 in the regs.
You also need to comply with 543.1.1 (not a problem in this case)
If it is a buried earthing conductor you need to look further.
 
hello again,

can I use amp law A = W/V on three phase?
is it right:

three-phase supply of 400V and machine load 5kW;

5kW = 5000W; 5000/400 = 12.5A;

so design current (lb) = 12.5A?

Thanks,
 
on 3 phase, your 5kW is shared between the 3 phases so P = √3 VI. so I = 5000/ (1.732 x 400) = 7.215A

that's without allowing for any power factor correction.
 
each phase will be 7.215A. so you select your cable and MCB accordingly. bear in mind that a motor draws a high start up current and will generally require a type C MCB.
 
if the load is a motor, the pf will be between 0.8 and 0.9 ish. so then divide the current by 0.8 to allow for this. in the above case, your current would then be 9A.
 
If you have no info on protective devices then you will just have to look into the regs book for min CSA which I think is 16mm for 25mm incoming and is this the type of questions that are in the tasks as I have just started my 304 unit and the questions I have seen so far don't seem difficult at all
 
the pf is determined by the actual motor design. nothing in the regs. sometimes it's printed on the motor rating plate. if not, then you have to make an educated guess. 0.8 is about the worst you'll get so if you use that value, you''ll be erring on the side of caution.
 

Reply to Studies Help Please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
No live and neutral at the wall. But that would be the switch live right?
Replies
14
Views
1K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
690

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top