J

Joe Johnson

Hi I wonder if I could get a few opinions, randomly half of my house shuts off or flickers, this included the stove, lights, fans, clocks etc, then a minute or two later it comes back on, but no breakers ever trip. I had an electrician out and he suggested a loose neutral but never actually fixed anything. It is very random, sometimes doesn't happen for months then starts back up again. Any thoughts? Its not something I will attempt to fix but I'd like to have some thoughts before speaking to an electrician as the last guy seemed to think it was specific to an outlet or switch but couldn't explain how that would shut the stove off. Hydro was out and confirmed power to the meter was as expected but the randomness of the problem wasn't occurring while he was present.
 
Last edited by a moderator:
Mains voltage in Canada is 120V. If split phase 120-0-120V supplies are used, as in the USA, then it's probably a fault with one of the supply phases.
Last time I had this in the UK, the cause was transformer pole fuses that were too short in length, packed out with (corroding) 2p coins.
 
As I wrote above then, but probably for a different reason.
Anything from, and including, the main switch backwards to where your supply connects to the supply to other properties, assuming you are the only one affected. Have you checked with neighbours?
 
What was that 'electrician' thinking?

One side of the panel fed by one hot leg / phase is OK.
One side of the panel fed by the other hot leg / phase is intermittent.
No breakers trip.

With 99.9% certainly the problem is upstream of the panel busbar and is a bad connection in the phase that is intermittent. Could be one of your components e.g. main breaker, or could be one of Hydro's e.g. meter socket. But it's not likely to be the neutral and it certainly isn't anything downstream of the busbar e.g. one of the ordinary breakers. The bad connection might already be overheated, discoloured, burnt etc. and might respond to wiggling.

Unless something very spooky is going on, this shouldn't have anyone stumped for long.
 
What was that 'electrician' thinking?

One side of the panel fed by one hot leg / phase is OK.
One side of the panel fed by the other hot leg / phase is intermittent.
No breakers trip.

With 99.9% certainly the problem is upstream of the panel busbar and is a bad connection in the phase that is intermittent. Could be one of your components e.g. main breaker, or could be one of Hydro's e.g. meter socket. But it's not likely to be the neutral and it certainly isn't anything downstream of the busbar e.g. one of the ordinary breakers. The bad connection might already be overheated, discoloured, burnt etc. and might respond to wiggling.

Unless something very spooky is going on, this shouldn't have anyone stumped for long.
Wow, that’s the answer hoping for, a confident one! Now at least I can have this conversation with the electrician, thanks a bunch Lucien!
 
Hi I wonder if I could get a few opinions, randomly half of my house shuts off or flickers, this included the stove, lights, fans, clocks etc, then a minute or two later it comes back on, but no breakers ever trip. I had an electrician out and he suggested a loose neutral but never actually fixed anything. It is very random, sometimes doesn't happen for months then starts back up again. Any thoughts? Its not something I will attempt to fix but I'd like to have some thoughts before speaking to an electrician as the last guy seemed to think it was specific to an outlet or switch but couldn't explain how that would shut the stove off. Hydro was out and confirmed power to the meter was as expected but the randomness of the problem wasn't occurring while he was present.
You are definitely loosing 1 leg of your hots coming in. If it was the neutral loose then everything would be acting up. It could actually be on the power company’s side, it could also be in the meter base, and it could also be a defective main breaker. Hire you another electrician and let him read this post. Good luck and let us know how it turns out.
 
You are definitely loosing 1 leg of your hots coming in. If it was the neutral loose then everything would be acting up. It could actually be on the power company’s side, it could also be in the meter base, and it could also be a defective main breaker. Hire you another electrician and let him read this post. Good luck and let us know how it turns out.
awesome thanks!
 
awesome thanks!
Dear Joe, has the issue been repaired? As, a technician, I experienced a fault, similar to this, in a farmhouse,
once in Essex, putting aside some very technical, reasons, consider keeping it to any simple causes, as well.
You have an intermittent fault, causing flickering, and "brown outs", i.e. not completely off, or trip of breaker.
Is this happening, in wet weather? In the farmhouse, rainwater, on a broken light fixture, did the short circuit.
It can be a general property maintenance issue, suggest checking, for any rainwater ingress, or a pipe drips.
Could also, be caused by a bathroom remodel, where fitter has not waterproofed, or capped old wiring right.
 

Reply to Stumped my electrician in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
The rent deposit schemes are very "Pro" tenant . And tend to always believe a tenant more than a landlord . With smart phones been almost a common...
2
Replies
29
Views
3K
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top