L
Londonsparky
Stupid question but can you connect swa to flex cable via a 15/5amp terminal block in a waterproof terminal box?
Tom
Tom
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Stupid question swa to flex via terminal block in the Australia area at ElectriciansForums.net
Yes.
for example, use one these...
25mm 2 Way Galvanised Conduit Box | *************
with appropriate glands for the SWA & flex
&
assuming the cables are the same csa.
also read this, substitute silly with stupid...
http://www.electriciansforums.net/e...l-forum/29586-silly-questions.html#post232904
Good forum this!
And use a ''cast lid'' with gasket, and brass screws, if being externally mounted, ....not the usual thin metal plate lid variety!!
Reply to Stupid question swa to flex via terminal block in the Australia area at ElectriciansForums.net