DD1990
ok so im working in a property and the lady has a 16A RCBO on the RCD side of the fuse board in her house... it feeds a 100A 5way rcd CCU in her garage supplied by 2.5 SWA... everything in the garage turns on fine but when you plug anything into a socket it bypasses the 100A RCD in the garage and the RCBO in the house but trips the RCD in the house... if you take the RCBO neutral out and put it on the non RCD side of the house fuse board everthing works fine but you get a loop reading of 1.31ohms....overly confusing any help would be great.
N-E fault in garage. Whoever decided to put three RCDs in series though is an absolute moron! When you've sorted out the fault in the garage, connect the submain to an MCB on the non RCD side of the main DB, and make sure the MCB is connected to the busbar correctly, I suspect your higher Zdb is because the RCBOs clamp had missed the busbar.
Reply to Sub board in garage in the UK Electrical Forum area at ElectriciansForums.net
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...