E
energizedelec
iv been asked to install a sub-main to supply a house. The supply is quite far away from the house (40mtr) the cable will be installed direct in ground (SWA)
im abit rusty on my cable calcs and could do with some help and advice. hear is where i am at the moment...
ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.
then volts drop mv/a/m = 1.75
so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v
now if it was a final circuit not for lighting this would be ok (as it doesnt exceed 11.5v 5%). but its for a distribution circuit so if i was to then have other circuits running of it the volts drop would increase how do i account for this??
Read more: http://www.electriciansforums.net/e...3-supply-calculations-help.html#ixzz22QGLTbuq
im abit rusty on my cable calcs and could do with some help and advice. hear is where i am at the moment...
ok so after applying diversity Ib = 91.5A and In=100A
so from table 4d4a multi-core armored 70'c refrence method D you get 99A for 25mm cable.
then volts drop mv/a/m = 1.75
so...
1.75 x 91.5A x 40 mtr /1000 to convert to volts = 6.405v
now if it was a final circuit not for lighting this would be ok (as it doesnt exceed 11.5v 5%). but its for a distribution circuit so if i was to then have other circuits running of it the volts drop would increase how do i account for this??