Scott89

Hi guys iv been asked to put a sub main in 80 meters away!
It will need to have
1 x 32amp with 8sockets on
3 x 10amp with heater on each mcb
1 x 6amp with 8 lights on

Please give me your thoughts on cable size thanks guys
 
Look in BS 7671, all you need to know is in there. Work out your design current, apply correction factors, select appropriate overcurrent and earth fault protection, select appropriate size cable, confirm adequate size CPC (if not rodding), confirm voltage drop is within permitted values, if not, upsize until it is.
 
Hi Scott think your getting the theme here we don't spend 4yrs in college to give out all the calcs to any Tom, Dick or Harry..... as others have suggested you need to show us your calcs and we will be happy to help, your info given is lacking vital parts to even attempt a calc refer to your notes on cable calcs supply us with all the info and ask where you are getting stuck and help will be here but not as in you OP suggests.... do all this for me please because I either can't or can't be bothered.
 
Ok I understand where you guys are coming from. My thoughts are my load is going to be 70amps and I was thinking of putting a 25mill armoured 3core cable because of volt drop for lighting ect, I haven't done a proper calcs yet, i was just seeing if anyone had any advice. So looks like ill do my calc when I get home
 
I assume a little diversity can be applied as your heating is accounted for and unless your telling us otherwise I doubt the sockets will be loaded 32amps.... also yes do calcs first although your drip feeding us info we now know its a swa .... bt is it buried ?
 
Now you've been given a few tips ... do the calcs and show us your thoughts when you get time... might seem im been harsh but its best way to learn how to do it yourself if we simply got the info and give you an answer then you will always depend on others in similar situations and never really get a full grasp of it. .....80m is a good distance and at 80amps if you used this in calcs you'll surprise yourself how much larger the cable is required due to volts drop although I assume 1ph? with your random guess of 25mm .... you see now we lack a lot of info'
 

Reply to Sub main for garage 80 meters away in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
166
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
290

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top