Pmarsh

Hi all,

I have a sub main installation 30 metres from source on a supply that is generated from solar with a TT earthing arrangement.

My question is would it be sufficient to protect the cable to the sub-main with a 40a MCB from the non RCD side of the plastic ( customer doesnt want an upgraded board fitting ) original board at the house. or is it absolutely necessary to have an RCD behind it also.
I've read about 100ma S type time delayed RCDs but would it be sufficient with just an MCB

The CU at the sub main end will be metal, the cable run SWA 10mm underground, an earth rod will also be used for earthing at the sub main end, I was going to earth the armour at the sub main end as it will be insulated at the plastic board at the house. the circuits will be 40A/30maRCD with two finals lighting 6A and radial 16A

Assessor out to see work to sign up, is overload protection on the supply cable acceptable?

thanks in advance
 
Its just PV and win generation to a bank of batteries completely off the grid so Ze will be low, spoke to someone today on it and they seem to think what i'm proposing is fine, 40A MCB in db, 10mm SWA underground at decent depth to sub main CU earth the armour both ends with 6mm and final ccts will consist of 40A-30ma-RCD 6A-MCB-lighting 16A-MCB-Radial.

Not going to bother with an earth rod at the Sub-main end incase it introduces a potential difference and negatively effects the RCD

10mm earth and armour earthing should be sufficient for the intended run.
What are your thoughts interested to know, 6 years of my career has been in substations therefore the 17th regulations are loosely followed within the network due to the age of the installations.
 
Its just PV and win generation to a bank of batteries completely off the grid so Ze will be low, spoke to someone today on it and they seem to think what i'm proposing is fine, 40A MCB in db, 10mm SWA underground at decent depth to sub main CU earth the armour both ends with 6mm and final ccts will consist of 40A-30ma-RCD 6A-MCB-lighting 16A-MCB-Radial.

Not going to bother with an earth rod at the Sub-main end incase it introduces a potential difference and negatively effects the RCD

10mm earth and armour earthing should be sufficient for the intended run.
What are your thoughts interested to know, 6 years of my career has been in substations therefore the 17th regulations are loosely followed within the network due to the age of the installations.

The submain would be better off being protected by an HRC fuse for discrimination.
 
Does this installation even have a Ze? With no external supply how can there be an external loop impedance?

The big question in my mind is what fault current is available? It's almost certain that the inverter will not supply enough fault current to operate an ocpd and so other means of earth fault protection will be needed
 
http://www.solarcharge.com.au/docs/SB1200SB1700SB2500SB3000.pdf
this is the inverter, which wattage it is I'm unsure as it isn't written on it anywhere.
Theres also a bank of about 10 large batteries of which I'm not sure of the amp/hr without a re-visit which is looking likely.

Murdoch, nuisance tripping of the rcd in sub main board I was referring to with the Earth rod and possible introduction of a potential difference

might it be an idea to add the 40a to the rcd side of the house board then? Or seperate rcbo.
 
http://www.solarcharge.com.au/docs/SB1200SB1700SB2500SB3000.pdf
this is the inverter, which wattage it is I'm unsure as it isn't written on it anywhere.
Theres also a bank of about 10 large batteries of which I'm not sure of the amp/hr without a re-visit which is looking likely.

Murdoch, nuisance tripping of the rcd in sub main board I was referring to with the Earth rod and possible introduction of a potential difference

might it be an idea to add the 40a to the rcd side of the house board then? Or seperate rcbo.

Hum... best you read up on how RCD's work then before making any changes....
 

Reply to Sub Main MCB supply cable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for all comments still debating how to solve this, i personally would install MCB, having an idea the cable is installed under...
Replies
11
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top