Pmarsh
Hi all,
I have a sub main installation 30 metres from source on a supply that is generated from solar with a TT earthing arrangement.
My question is would it be sufficient to protect the cable to the sub-main with a 40a MCB from the non RCD side of the plastic ( customer doesnt want an upgraded board fitting ) original board at the house. or is it absolutely necessary to have an RCD behind it also.
I've read about 100ma S type time delayed RCDs but would it be sufficient with just an MCB
The CU at the sub main end will be metal, the cable run SWA 10mm underground, an earth rod will also be used for earthing at the sub main end, I was going to earth the armour at the sub main end as it will be insulated at the plastic board at the house. the circuits will be 40A/30maRCD with two finals lighting 6A and radial 16A
Assessor out to see work to sign up, is overload protection on the supply cable acceptable?
thanks in advance
I have a sub main installation 30 metres from source on a supply that is generated from solar with a TT earthing arrangement.
My question is would it be sufficient to protect the cable to the sub-main with a 40a MCB from the non RCD side of the plastic ( customer doesnt want an upgraded board fitting ) original board at the house. or is it absolutely necessary to have an RCD behind it also.
I've read about 100ma S type time delayed RCDs but would it be sufficient with just an MCB
The CU at the sub main end will be metal, the cable run SWA 10mm underground, an earth rod will also be used for earthing at the sub main end, I was going to earth the armour at the sub main end as it will be insulated at the plastic board at the house. the circuits will be 40A/30maRCD with two finals lighting 6A and radial 16A
Assessor out to see work to sign up, is overload protection on the supply cable acceptable?
thanks in advance