Sub-main to the garage in house I just bought | on ElectriciansForums
Discuss Sub-main to the garage in house I just bought in the UK Electrical Forum area at ElectriciansForums.net
North west
Hello all.
17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident).
Just bought a house with a 16mm 3 core SWA, 15m long, clipped around the side of the house low level. This feeds the double garage.
It has it's own 100A fused isolator in a kitchen cupboard (behind the meter box) with a 63A HRC fuse in it. 25mm tails (16mm earth) come from a couple of DP connection blocks in the meter cupboard.
Garage end has a 12 way split load metal DB with 2x 63A RCD's and is only feeding a couple of sockets on a 16A radial and the lights on a 6A.
My question. Not being up to date now on the 18th, should that external SWA sub-main be protected by an RCD?
Reason I am asking is I want to have a car charger added to the garage and that has it's own internal RCD (They are fitted by a local company as part of the car purchase deal). The board in the garage would be re-arranged so that a 32A MCB would be after the main switch (not on the split load).
Thanks from a slightly broken old sparky
Without knowing thr age of the house it'd be hard to say, I think RCDs on everything was recent (2018) if so yhrn you've got the "Complied at time of erection" argument.
Either whack an RCD on the garage circuit in thr main board or leave it off an RCD in tht House and put a Type A in at the garage end, although Check your EV kit manual as they may want a different setup.
Still Lear ing so happy to be corrected
Unless I'm much mistaken, no it doesn't need an RCD on the SWA submain. The SWA has earthed metallic covering which is one of the factors that negates the requirement for RCD.
533.6.204 (i) incorporate an earthed metallic covering which complies with the requirements of these regulations for a protective conductor of the circuit concerned, the cable complying with BS 5467, BS 6724, BS 7846, BS 8436 or BS EN 60702-1, or (one of the other conditions).
So providing the armour is properly earthed, no problem.
The only circumstances I can currently see it needing an RCD for fault protection would be if the house had TT earthing.
15m of 16 sq mm SWA wouldn't otherwise have a problem with the fault current failing to blow a 63A fuse.
Maybe your Ze is 0.80 ohm😁
Even if the Zs is sufficiently low not to require additional protection it wouldn't do any harm to install a 100ma S type RCD at the switch fuse end, just in case of failure of the downstream RCD/s.
If we worried about devices failing we would be backing everything up.
The Zappi car charger recommends no RCD's before it, as its just been updated to comply with the 18th and has it's own RCD.
Link here to the charger they are installing.
It's probably been installed a while (although the metal split load board in the garage looks newish).
TNS supply.
I'll leave it be. Seems well enough installed. No certs for it I did notice.
I’m not surprised there’s no certs.
16mm for a couple of sockets?
Either all someone had in the van, or they really did think ahead, for the chance that maybe a future owner would like an EV.
Hey all. I didn't start a new thread, as it's kinda the same subject.
Went around my bosses house yesterday and looked at his car charger install.... Hmm.
He has a 6mm 3 core SWA running clipped outside for about 10m. Feeds his garden office in which he only has a couple of lights and a a few sockets. Not much load and he is rarely in there.
The sparky has put a 32A MCB type B at the board end (apparently it used to be an RCBO), and this now feeds the 9 way board in his office.
The 9 way board has 100A isolator, SPD with it's own 32A MCB, then an MCB for the Zappi car charger (which has it's own internal RCD), and then after that.... a 63A RCD that protects the rest of the board with a 16A and 6A for the lights and power in the office.
Is that pushing the limits of a 6mm 3 core SWA? Granted the Zappi is set up to never allow more than 32A to be pulled.
Personally, I would have upgraded the 6mm to something bigger, but apparently it was done 'on a budget'.
Thoughts?
Reply to Sub-main to the garage in house I just bought in the UK Electrical Forum area at ElectriciansForums.net
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...