hey guys
im a bit confused about testing submains, never had to do any untill now.
2way board in the garage fed off a 32a mcb in house
the zs for the garage circuit will become the zdb?
do i still measure pfc pss at the submains?
napit assesment soon double checking everything
cheers
Hey Bahco.
On the test cert there should be boxes under the heading of "chracteristics at this distribution board" this is where you insert the Zs and PSC values at the dis board in your garage.
Hope this helps.
hey lenny
still confused tbh
so my plan is to issue a eic cert with 2 test sheets
1 for the circuit supplying the garage
1 for the 2 circuits in the garage
so when i test zs of circuit supplying the garage that will then become my zdb on my 2nd sheet of test rusults
so do i still need to test for pfc in garage or is that just done at origin?
cheers
Hey.
You need to treat the garge DB as a DB in it's own right, so you would measure Zs and PSC at this board and put it on the cert seperately from the origin.
On the test from, the very top line on the test res sheet is set aside for details of the sub-main circuit (if any) supplying it. this is where you detail the cable type, inst method and record all test res I/R, R1+R2, Zs etc.
PSC is then noted at the bottom of the sheet alongside DB designation and location, or at least this is how NIC forms are laid out.