A

allybally

I have a Job to supply a kitchen with power, the board will be 20m from the main head and will be mainly run surface/trunking and under floors (no insulation), I'm thinking of using either 10/16mm2 t&e all will be rcd protected, but my question is...

I have a spool of 6mm2 t&e, could I run a ringmain, so 12mm2 cable supplying the new kitchen board? Just a thought to save some money but not sure if it would be simple thing that would get pulled up in an inspection

Many thanks

Tns system, with no bonding at the kitchen end
 
yes you can run 2 feeds in parallel so long as theyre the same length , which they will be.

i'd be surprised that just 1 6mm cable wont do the job if its only sockets , lights & appliances , and theres no electric hob.
 
Thanks for the reply, it's a kitchen in a music school, they have a

3kw earn,
a 2.5kw air con / heater
2 x standard kettles
And 3 toasters

So a fairly heavy load ( the kitchen feeds up to 45 people so all is being used for a good hour at least)
 
So yeah I'd say about 50A total load on the board, and I take it I'm right in saying 1 x 6mm2 cable can take 32A then 2 x 6mm2 cables will be 64A, run reference method A, above ceiling
 
Thanks for the reply, it's a kitchen in a music school, they have a

3kw earn, 3000
a 2.5kw air con / heater 2500
2 x standard kettles 4000
And 3 toasters 3000

total 12500 w

12500w / 230v = 54A
i'd apply diversity of around 70% for that lot so

54 x 0.7 = 38A total demand

current capacity of 6mm t&e ref C clipped direct = 47A

check volt drop ; 7.3 mv / A / mtr = 7.3 x 38 x 20 / 1000 = 5.5v drop ( o.k. )


So a fairly heavy load ( the kitchen feeds up to 45 people so all is being used for a good hour at least)

sometimes its best to work it out rather than guess ;-)
 
Yeah I'm going to have the cable supplying the kitchen in a RCD and MCB, then just a main switch with MCB at the CU, I did think about armoured but the rating isn't clear in the regs, and t&e would be easier to run, but I'm open to any help and advice, it's not everyday you get such a large kitchen demand
 
Thanks that's a great post, and diversity on a commercial scale kitchen, can you or should you allow for that? And would you call above ceiling the same as clipped direct? I jut don't want to screw this cable up, many thanks
 
Thanks that's a great post, and diversity on a commercial scale kitchen, can you or should you allow for that?
i already allowed for that with a generous 0.7 factor.

And would you call above ceiling the same as clipped direct?
yes so long as its not covered in insulation
I jut don't want to screw this cable up, many thanks

..............
 
even though ive shown the supply will work with 6mm , i do admit its tight with little room for expansion.
best bet would be 1 x 10mm on a 50a mcb , maybe put 2x 6mm cables in anyway to save hassle from unexpected surprises later.
i just thought id show you through the process ;-)
 
Run a 10 mm preferably SWA, or T&E!! At least that will give you some sort of headroom for any future additional appliances like a small oven or 2 ring hot plate and the like!!
 

Reply to Submain cable ideas? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288
  • Question
https://www.d-line-it.com/u-clips/
2 3
Replies
31
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top