Right, I'll try to keep this simple.

I have a job coming up that involves installing a couple of storage heaters. The 2 rooms are on the 2nd floor of an old building and the DB is in the basement. They also require a ring main to give power to the 2 rooms.

There is no way of running cables back to the DB as this would create a lot of extra work which they can't have done as the premises is in constant use.

My plan is to wire the neccesarry circuits on the their own DB and run a Submain back to the original DB down the side of the building and into the basement.

How do I calculate what size cable I need for this. It's a while since I did this. I've worked out my cable calcs for the necceassary circuits.

I'll have 2x 16A for the heaters and 1x32A for the sockets.
 
Sub Main calc

Right, I'll try to keep this simple.

I have a job coming up that involves installing a couple of storage heaters. The 2 rooms are on the 2nd floor of an old building and the DB is in the basement. They also require a ring main to give power to the 2 rooms.

There is no way of running cables back to the DB as this would create a lot of extra work which they can't have done as the premises is in constant use.

My plan is to wire the necessary circuits on the their own DB and run a Sub Main back to the original DB down the side of the building and into the basement.

How do I calculate what size cable I need for this. It's a while since I did this. I've worked out my cable calcs for the necessary circuits.

I'll have 2x 16A for the heaters and 1x32A for the sockets.
 
Calculate the maximum load that is going to be on thses two rooms including the heaters. Then chose your cable size for the submain. I would use a 16mm T+E it might sound a bit overkill but it will give you plenty of scope should there be any more added to that con/unit.
 
How big are the rooms and what are they going to be used for?

Do you really need a 32A socket circuit for 2 rooms. Wouldn't a 20A radial suffice?
 
How big are the rooms and what are they going to be used for?

Do you really need a 32A socket circuit for 2 rooms. Wouldn't a 20A radial suffice?


A 20A radial probably will do to be honest. I'm just rough planning for it at the moment so didn't pay too much attention to that.
 
Do you know how much power the storage heaters actually use?

How long is your sub-main feed going to be? Important for Voltage Drop calculation etc.

What cable are you using for the sub-main? If I've understood your post, you're running it outside.
 
Do bear in mind that the storage heaters will not be in powered during normal office hours (unless they`re on economy 10 or 11 tariffs), so you dont need to be too generous in sizing your submain
 
Do bear in mind that the storage heaters will not be in powered during normal office hours (unless they`re on economy 10 or 11 tariffs), so you dont need to be too generous in sizing your submain

If he's running them off the same CU as the sockets I would presume they will have power available all the time, so they would either have to be switched on and off manually or run off a timer of some sort.
 
Re: Sub Main calc

There are several things that need to be determined here MUFC1999.

The sub main needs to be capable of carrying the tabulated currents of all circuits on the new DB. The new DB must now have RCD protection as required by BS7671.

The length of the sub main cable is very important because of voltdrop, which is now 3% for lighting and 5% for all other circuits. (correct me if im wrong anyone).

If you are taking the sub main capable outside the premises then l suggest that you use SWA cable. It may be expensive but its recommended for outdoors.

What wattage are the storage heaters, MUFC1999?
 
Re: Sub Main calc

jabberjaws.
The length of the sub main cable is very important because of voltdrop, which is now 3% for lighting and 5% for all other circuits. (correct me if im wrong anyone).


you are correct with that satement however that is total drop from origin (meter). If its sub mains i reccomend doing the calcs for 1% or less for sub mains as it gves more leaway when doing the final circuits. and it may only increase the swub mains cable by 1 size .
 
The storage heaters are 2.55KW.

I'm fully aware that I'll need RCD protection and I will be running the Sub Main in SWA. I've not measured it yet but I reckon 20 meters will do it.
 
Assuming a design current of around 43A (20A for sockets and just over 22A for the storage heaters), I would go with 10mm² 3-core SWA (CCC Method C = 67A) using one of the cores as cpc.

Voltage drop for 20 meters = 4.4 x 43 x 20 Ă· 1000 = 3.8V leaving you 7.7V to play with for your final circuits.

Would depend if any lights are going to be fed from sub-main obviously.
 
Last edited by a moderator:
That's what I'd worked it out at just needed a second opinion. Like I said it's a while since I last did cable calcs.

Cheers for the help.
 

Reply to Submain calc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
943
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top