Hi All,
I have a theory, that in a small village with 2 substations, one substation has a good earth connection but the other has a high earth connection.
Some of the houses in the village use TT systems, the houses connected to substation 1 have a Ze of approx 6 ohms. The houses connected to substation 2 have a Ze of approx 600 ohm.
The distance between the substations is approx 500-600 metres.
Why worry I hear you say, most supplies could be changed to TN-C-S, this has been the case for most of the houses in the village, so change the rest to TN-C-S and hey presto, everything is happy. No!
There is a caravan park (touring caravans) connected to substation 2 (the bad earth).
Would you agree that the substation earth connection is at fault?