Suitable testing instruments | on ElectriciansForums
Discuss Suitable testing instruments in the UK Electrical Forum area at ElectriciansForums.net
H
Haydenr25
Hey guys, I need help finding out which tester you'd need to test for: continuity of circuit protective conductors, earth fault loop impedance and prospective fault current. I'm pretty sure you'd use a low reading ohmmeter for continuity but I don't know the other two. Also, any requirements from GS 38 for these test instruments? con
You should be able to find all the answers you need in Guidance note three.
This describes the tests and the instruments required.
A little bit of checking and you would have the answer.
Low resistance ohmmeter
Earth fault loop impedance tester
GS38 applies to test instruments for electricians that may present a risk.
Generally this means that anything apart from a low resistance ohmmeter needs to comply with GS38.
GS38 is available for free download from the HSE website
Reply to Suitable testing instruments in the UK Electrical Forum area at ElectriciansForums.net
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!