Q36 state two reasons for confirming the value of Ze for a new installation
A36 (i) to verify the existence of a supply to earth
(ii) to verify that the Ze is not greater than the value used in any of the design calculations, this value can be added to R1+R2 values to give a Zs value for individual circuits
Q37 A circuit is protected by a TYPE C circuit breaker and is just over the maximum allowed earth fault loop impedance value. List three possible solutions to get the required disconnection time
A37 (i) try a TYPE B circuit breaker if load characteristics allow the maximum Zs for a TYPE B circuit breaker
is twice that for a TYPE C
(ii) use a RCD or RCBO with suitable ratings
(iii) use circuit conductors with a larger C.S.A to reduce Zs
Q38 list six things to be checked before using a low resistance ohmmeter and leads
(i) Check condition of meter
(ii) Check the meter is within calibration date
(iii) Check the battery
(iv) Check the instrument is zeroed
(v) Check the condition of the leads and probes
(vi) Check the resistance of the leads and probes is nulled out
Q40 state the BS number of those Edison lampholders to which the polarity check does not apply in normal circumstances
A40 The check is not required for E14 & E27 lampholders to BS EN 60238
Q41 State the maximum allowable disconnection times for the following 230V a.c. circuits
A. 6A lighting circuits in a TN- S installation
B. Distribution circuits in a TN-S installation
C. 32A ring final circuits in a TT installation
A41 A. 0.4 s
B. 5 s
C. 0.2 s
Q42 state the maximum allowable rating for a RCD used for:-
A. Additional protection
B. Fire protection on a farm
A42 A. 30mA
B. 300mA
Q43 state the maximum recommended value for the resistance of an earth electrode for a TT installation protected by a RCD
A43 200Ω
A36 (i) to verify the existence of a supply to earth
(ii) to verify that the Ze is not greater than the value used in any of the design calculations, this value can be added to R1+R2 values to give a Zs value for individual circuits
Q37 A circuit is protected by a TYPE C circuit breaker and is just over the maximum allowed earth fault loop impedance value. List three possible solutions to get the required disconnection time
A37 (i) try a TYPE B circuit breaker if load characteristics allow the maximum Zs for a TYPE B circuit breaker
is twice that for a TYPE C
(ii) use a RCD or RCBO with suitable ratings
(iii) use circuit conductors with a larger C.S.A to reduce Zs
Q38 list six things to be checked before using a low resistance ohmmeter and leads
(i) Check condition of meter
(ii) Check the meter is within calibration date
(iii) Check the battery
(iv) Check the instrument is zeroed
(v) Check the condition of the leads and probes
(vi) Check the resistance of the leads and probes is nulled out
Q40 state the BS number of those Edison lampholders to which the polarity check does not apply in normal circumstances
A40 The check is not required for E14 & E27 lampholders to BS EN 60238
Q41 State the maximum allowable disconnection times for the following 230V a.c. circuits
A. 6A lighting circuits in a TN- S installation
B. Distribution circuits in a TN-S installation
C. 32A ring final circuits in a TT installation
A41 A. 0.4 s
B. 5 s
C. 0.2 s
Q42 state the maximum allowable rating for a RCD used for:-
A. Additional protection
B. Fire protection on a farm
A42 A. 30mA
B. 300mA
Q43 state the maximum recommended value for the resistance of an earth electrode for a TT installation protected by a RCD
A43 200Ω