hello
i would like to know maximum zs at the sub board !
i used the house otside socket feed to summer house!
i connected one outdoor fused spur under the socket ,with 13a fuse!and that feed small fuseboard in the summer house!
1-6a lighting
1-10a socket circuit!
i took the zs reading at the socket (0,45 ohm)
in this case how much is the maximum zs at the S.H.distribution board allowed,permitted?
thank you!
 
YES IT HAS 30 MA RCD

So why have you also put a 30mA RCD in the sub board in the summer house.
Surely the best set up for this would have been to go from the outdoor socket, into a 13A FCU, Straight into the summer house socket with the light coming off a 3A FCU next to the summer house socket?
 
So why have you also put a 30mA RCD in the sub board in the summer house.
Surely the best set up for this would have been to go from the outdoor socket, into a 13A FCU, Straight into the summer house socket with the light coming off a 3A FCU next to the summer house socket?
YES! YOU ARE RIGHT! BUT WHAT THE PROBLEM WITH THE SUB FUSEBOARD IF THE CUSTOMER ALREDY BOUGHT THAT! I DONT WANA SAY I DONT CONNECT IT UP!
I CANT SEE ANY ISUE FOR THE SUB BOAR! OR YOU CAN SEE THE PROBLEM?
 
YES! YOU ARE RIGHT! BUT WHAT THE PROBLEM WITH THE SUB FUSEBOARD IF THE CUSTOMER ALREDY BOUGHT THAT! I DONT WANA SAY I DONT CONNECT IT UP!
I CANT SEE ANY ISUE FOR THE SUB BOAR! OR YOU CAN SEE THE PROBLEM?
You should see the section in BS7671 about RCD selectivity if you have 2 30mA RCD devices in line with each other.
 
YES! YOU ARE RIGHT! BUT WHAT THE PROBLEM WITH THE SUB FUSEBOARD IF THE CUSTOMER ALREDY BOUGHT THAT! I DONT WANA SAY I DONT CONNECT IT UP!
I CANT SEE ANY ISUE FOR THE SUB BOAR! OR YOU CAN SEE THE PROBLEM?


I would have told the customer to take it back. You now have 2 30mA RCDs in place along with a 10A MCB for a twin socket, that’s likely to trip. Also a Sub Board fed off a existing socket circuit, I’m sorry isn’t for me at all.
 

Reply to Sumer house -sub board Zs!? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top